Old 04-27-2012, 08:49 PM   #1
Senior Member
 
MHElectric's Avatar
 
Join Date: Oct 2011
Location: NC
Posts: 1,274
Default Dining room and breakfast nook circuit

Does anybody pull this in #12? Ive been all through art. 210, I don't see this being a requirement anywhere, and yes, it is being enforced in an area I am working. I always welcome someone showing and explaining something new to me from the code.

__________________
Commit to the Lord whatever you do, and your plans will succeed.
MHElectric is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 04-27-2012, 08:55 PM   #2
Senior Member
 
Join Date: Sep 2010
Location: Wisconsin
Posts: 228
Default

210.52(B)(1) says the 2 or more sabc's shall serve the dining room.

Mulder is offline   Reply With Quote
Old 04-27-2012, 08:58 PM   #3
Chief Electron Relocator
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 31,291
Default

I would hope you pull 12.

210.52(B)(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.

210.11(C) Dwelling Units. (1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
__________________
In winter, why do we try to keep the house as warm as it was in summer when we complained about the heat?
480sparky is offline   Reply With Quote
The Following User Says Thank You to 480sparky For This Useful Post:
Magnettica (04-28-2012)
Old 04-27-2012, 09:05 PM   #4
Good at being Evil
 
Shockdoc's Avatar
 
Join Date: Mar 2010
Location: Long Island,NY & Poconos
Posts: 11,119
Default

And AFCI protected as of 11'.
__________________
All these liberal laws has turned me into a right wingnut..
Shockdoc is offline   Reply With Quote
Old 04-27-2012, 09:52 PM   #5
Senior Member
 
MHElectric's Avatar
 
Join Date: Oct 2011
Location: NC
Posts: 1,274
Default

Quote:
Originally Posted by 480sparky View Post
I would hope you pull 12.

210.52(B)(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.

210.11(C) Dwelling Units. (1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
I took this as the dining room was aloud to be on the kitchen sabc, but I put it on its own circuit instead. Unfortunately I pulled it in #14. The inspector turned it down, and we spent this morning fixing it.

......another lesson learned the hard way.....
__________________
Commit to the Lord whatever you do, and your plans will succeed.
MHElectric is offline   Reply With Quote
Old 04-27-2012, 09:53 PM   #6
Good at being Evil
 
Shockdoc's Avatar
 
Join Date: Mar 2010
Location: Long Island,NY & Poconos
Posts: 11,119
Default

Quote:
Originally Posted by MHElectric View Post
I took this as the dining room was aloud to be on the kitchen sabc, but I put it on its own circuit instead. Unfortunately I pulled it in #14. The inspector turned it down, and we spent this morning fixing it.

......another lesson learned the hard way.....
The only #14 you can use in there is for fixed lighting.
__________________
All these liberal laws has turned me into a right wingnut..
Shockdoc is offline   Reply With Quote
Old 04-28-2012, 10:01 AM   #7
Professional Nit Picker
 
manchestersparky's Avatar
 
Join Date: Mar 2007
Location: Manchester ,Maryland
Posts: 1,307
Default

Quote:
Originally Posted by Shockdoc View Post
And AFCI protected as of 11'.

Required as of 2008
__________________
Anything Worth Doing ....
Is Worth Doing Right
manchestersparky is offline   Reply With Quote
Old 04-28-2012, 10:21 AM   #8
Chief Electron Relocator
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 31,291
Default

Quote:
Originally Posted by MHElectric View Post
I took this as the dining room was aloud to be on the kitchen sabc, but I put it on its own circuit instead. Unfortunately I pulled it in #14. The inspector turned it down, and we spent this morning fixing it.

......another lesson learned the hard way.....

It can be on one of the two SABCs. It just needs to be AWG12/20a. You're legal pulling in a third/fourth/fifth SABC if you want to.
__________________
In winter, why do we try to keep the house as warm as it was in summer when we complained about the heat?
480sparky is offline   Reply With Quote
The Following User Says Thank You to 480sparky For This Useful Post:
MHElectric (04-28-2012)
Old 04-28-2012, 10:26 AM   #9
Senior Member
 
MHElectric's Avatar
 
Join Date: Oct 2011
Location: NC
Posts: 1,274
Default

Quote:
Originally Posted by 480sparky View Post
It can be on one of the two SABCs. It just needs to be AWG12/20a. You're legal pulling in a third/fourth/fifth SABC if you want to.
Hind sight is 20/20. I misunderstood the wording on this. Wish I had of asked this question before I pulled it.
__________________
Commit to the Lord whatever you do, and your plans will succeed.
MHElectric is offline   Reply With Quote
Old 04-28-2012, 10:27 AM   #10
Chief Electron Relocator
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 31,291
Default

Quote:
Originally Posted by MHElectric View Post
Hind sight is 20/20. I misunderstood the wording on this. Wish I had of asked this question before I pulled it.

Most likely, your confusion arises from being told the myth that SABC's are for the countertops. I've heard that line over and over.
__________________
In winter, why do we try to keep the house as warm as it was in summer when we complained about the heat?
480sparky is offline   Reply With Quote
Old 04-28-2012, 10:42 AM   #11
Senior Member
 
Join Date: Aug 2011
Location: maryland
Posts: 641
Default

ty 480! I don't do houses anymore but this is the 2nd time this has come up this week on ET. It's something I wasn't aware of (shame on me) and very enlighting. I work commercial and brought this up at break time. No one belived me. They all said sabc was counter top only.
cultch is offline   Reply With Quote
Old 04-28-2012, 10:46 AM   #12
Chief Electron Relocator
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 31,291
Default

Quote:
Originally Posted by cultch View Post
ty 480! I don't do houses anymore but this is the 2nd time this has come up this week on ET. It's something I wasn't aware of (shame on me) and very enlighting. I work commercial and brought this up at break time. No one belived me. They all said sabc was counter top only.

I've often heard SABC's referred to as "Countertop Circuits".



When you encounter people like this, enlighten them with Charlie's Rule:

It doesn’t say what you think it says, nor what you remember it to have said, nor what you were told that it says, and certainly not what you want it to say. And if by chance you are its author, it doesn’t say what you intended it to say. Then what does it say? It says what it says. So if you want to know what it says, stop trying to remember what it says, and don’t ask anyone else. Go back and read it, and pay attention as though you were reading it for the first time.
__________________
In winter, why do we try to keep the house as warm as it was in summer when we complained about the heat?
480sparky is offline   Reply With Quote
Old 04-28-2012, 10:51 AM   #13
Senior Member
 
Join Date: Jan 2007
Location: California SFO bay area
Posts: 124
Default

Quote:
Originally Posted by 480sparky View Post
I've often heard SABC's referred to as "Countertop Circuits".



When you encounter people like this, enlighten them with Charlie's Rule:

It doesn’t say what you think it says, nor what you remember it to have said, nor what you were told that it says, and certainly not what you want it to say. And if by chance you are its author, it doesn’t say what you intended it to say. Then what does it say? It says what it says. So if you want to know what it says, stop trying to remember what it says, and don’t ask anyone else. Go back and read it, and pay attention as though you were reading it for the first time.
Charlie's Rule should be on Page One of the NEC, because it is so true. I can't count how many times I have had Charlie's Rule pop in my head before the code sec. I needed.
acrwc10 is offline   Reply With Quote
Old 04-28-2012, 05:27 PM   #14
RGH
Senior Member
 
RGH's Avatar
 
Join Date: Sep 2011
Location: NY
Posts: 2,349
Default

required since 08..but as an apprentice (30 yrs ago) I have always pulled a 20 amp cir for the dinning room....my master told me then as now people will put buffets out on the holidays..hot plates, slow cookers ect so he thought it was a good idea and then only pennies to run a 12 awg..funny how he had the foresight to see that applicaton...(he said)"last thing you want is someone M_fing you on xmas with cold food cause of a cir trip...and a house full of people"....old school common sense...
__________________
Are those doughnuts for anyone??

Last edited by RGH; 04-28-2012 at 05:29 PM.
RGH is offline   Reply With Quote
Old 04-28-2012, 06:49 PM   #15
PGW Professional
 
Magnettica's Avatar
 
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 12,782
Send a message via Yahoo to Magnettica
Default

The wording for this section could be better in my opinion. It's fair to assume that a small appliance will be in use in the ding room area. Coffee pot, stuff like that.

Magnettica is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dining Room Rec AFCI/GFCI Cletis NEC Code Forum 22 09-19-2011 09:00 AM
Add Living Room and Bathroom Circuit nchvac General Electrical Discussion 8 06-28-2011 05:27 PM
Dining room outlets - dedicated circiut? Two-headed boy General Electrical Discussion 5 05-24-2011 02:14 PM
Dining Room Circuit Chas Residential Electrical Forum 54 03-10-2011 08:57 PM
multiple room branch circuit Quinton688 General Electrical Discussion 16 12-01-2010 01:19 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 03:18 AM.


Electrician Talk © 2006 - 2010 The Building Network

Search Engine Optimization by vBSEO 3.6.0 RC 2