Old 12-04-2008, 11:48 PM   #1
Nosparxsse's Avatar
Default Disconnect or not??
Residential setting
House with basement.
200 amp meter socket on outside.
Used knockout in back of meter socket.
sch 40 PVC 90 down to basement with approx 24 in. of pipe between 90 from Meter socket and panel. total distance on wire, 55" long.
Code violation or ok?
no disconnect on outside, but within 5 ' of panel???
Nosparxsse is offline   Reply With Quote
Old 12-04-2008, 11:57 PM   #2
Chief Electron Relocator
Originally Posted by Nosparxsse View Post
Residential setting
What's your POCO rule?
It's 10' for me, and that only starts once you get inside the house. You can legally go 'round the house 5 times without a disco if you wanted to.
Old 12-05-2008, 12:05 AM   #3
chenley's Avatar
10' feet in the county and 36" in the city. <-- Two different POCO's
The way the OP stated I would not see it needing a disconnect. Althought, it is up to the POCO there.
Old 12-05-2008, 12:26 AM   #4
Nosparxsse's Avatar
5 feet
done this for years like this, but an inspector questioned me on it the other day..
pvc pipe is ok right???
code reference??
230.70 A (1) Everything is good there....
note: the pipe is passing through wood just above the basement wall plate, not concrete.
Old 12-05-2008, 04:28 AM   #5
kbsparky's Avatar
I'd say from your description that you have installed the Service Disconnect as soon as practical after the conductors have entered the building.
Acceptable to me and the inspectors around here. We've done this type of installation many times.
Old 12-05-2008, 05:57 AM   #6
gilbequick's Avatar
Here it's 6' total wire length, and I've never run it in PVC or any kind of pipe, I've just used 4/0 AL SE. But to have 6' end to end you've got to be pretty much back to back on your meter and panel.
Old 12-15-2008, 01:20 AM   #7
Listed & Labeled
Effectively Grounded's Avatar
Unless your Poco has their own rules for what happens AFTER the meter then it is subject to your inspectors opinion.
It sounds reasonable to me. General rule of thumb was always within 5' around these here parts
Effectively Grounded is offline   Reply With Quote
Old 12-15-2008, 12:46 PM   #8
I only have one queston in case I did miss it or not.,,
Did you have LB inside or just a 90° sweep ell ?
However in my area 6 feet is tyical limit but per POCO and Comm 16 { wisconsin state code } it stated 8 feet.
Merci,Marc
Old 12-15-2008, 01:12 PM   #9
Bkessler's Avatar
not.
When ls lunch?
Old 12-15-2008, 01:20 PM   #10
Originally Posted by Bkessler View Post
not.
Quoi ??? { What ?? }
Old 12-15-2008, 01:51 PM   #11
Bkessler's Avatar
My answer to the original question in the subject line.
When ls lunch?
Old 12-23-2008, 08:12 AM   #12
Nosparxsse's Avatar
Merci,Marc
meter,
pvc male adapter,
sweep 90,
coupling ,
18" of pvc,
male adapter,
panel.
in that order.....
The inspector DID finally agree that I was in the right, by the way... at least this time....
Old 12-24-2008, 11:15 PM   #13
You dont have any sch 40 exposed to physical damage, so that looks like a pretty good installation to me.
ralph is offline   Reply With Quote
Old 12-25-2008, 12:19 AM   #14
No LB, at least as far as I can tell from the picture anyway… Hopefully the conduit is plugged with duct seal where it leaves the back of the meter enclosure to prevent condensation and moisture accumulation in the panel below.
Old 12-27-2008, 06:53 PM   #15
8' here in state code like Marc said. Last summer I had to install a meter main and eat the cost because the power company said 80 feet was to far from the meter to the panel. On a job in spring with the same power company (different lineman) I was able to run around the house 80' before entering with no problem. So the POCO rules can change from one location to another.
John
jrclen is offline   Reply With Quote
Old 12-27-2008, 08:39 PM   #16
nap
a real PITA
POCO rules? Not around here. This is an AHJ situation and the POCO is not the AHJ.
sorry to hear about your grief from yet another entity. The inspectors can generally cause enough on their own.
and; no disco unless AHJ interprets this distance as too far.
Old 12-28-2008, 05:32 PM   #17
In this case the POCO just refuses to connect if they don't like something. And code has nothing to do with it. My problem is that the rules change from one neighborhood to another within the same POCO. What it amounted to in this case was a lineman with a big ego. And a supervisor back at the office who blindly backed him up.
John
Old 01-22-2009, 09:37 PM   #18
Residential setting
You should be okay because of the 25 ft tap rule
rbic102 is offline   Reply With Quote
Old 01-22-2009, 09:44 PM   #19
There's probably not an AHJ in this land that's going to let you run 25 feet of unprotected service conductors indoors.
In the original case, I'd call it fine. You installed that disconnect as close as practical after entering the basement. I get 3 feet here, but they'd pass that install too. I'm not sure how you'd even make that any more compact without mounting the panel crazy high (creating another violation).
Seems like the interpretation of how short "short" really is varies a lot. I've heard talk of AHJ's who want an outdoor disconnect for anything longer than a nipple indoors. If I have a case I think is borderline, I'll either install an outdoor disconnect anyhow, or see if I can get the inspector to swing by and look at it if the budget is a concern.
Old 01-22-2009, 10:31 PM   #20
I beg to differ with you. Where a panel cannot be placed directly behind the meter serving it you are allowed to run ser cable up to 25 feet without any protection . Been doing it for years and the code hasnt changed that. It is called a 25 foot tap rule where no protection is required on the service entrance conductors that can be no longer than twenty five feet from point of service attachment.
40 amp disconnect Absolutetruthz General Electrical Discussion 3 08-01-2008 10:08 PM
service disconnect location? electromanj Services and Service Equipment 15 06-07-2008 05:09 PM
Dishwasher disconnect... waco General Electrical Discussion 31 04-04-2008 09:53 PM
AC Disconnect Violation: MDShunk Code Violation Discussion 21 12-08-2007 11:21 PM
100 Amp Raintite Disconnect TIMJ3 NEC Code Forum 3 10-17-2007 10:28 PM