Old 08-23-2011, 04:44 PM   #1
Default Disconnect for VFD - Does it have to be within sight of VFD??
For years in industrial facilities, we have been able to disconnect a motor back at the MCC (and use LOTO) for service. We usually do this when the motors are located in Electrically classified spaces.
But also in pharmaceutical where the fewer boxes & conduits the better.
We were recently approached by a long term client about section 430.102 (A) 430.102 Location
(A) Controller. An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location.
There is an exception in 430.102 B 2 b. to allow LOTO for industrial installations. It is not clear if this exception is for motors only or controllers also.
slandau is offline   Reply With Quote
Old 08-23-2011, 06:51 PM   #2
Ax grinder
raider1's Avatar
The exception does not apply to controllers only to motors so if the VFD is the motor controller then you must have a disconnecting means located within sight of the VFD.
Chris
Old 08-23-2011, 07:43 PM   #3
Fluke Skywalker
walkerj's Avatar
Chris
What if the drive has a main disconnect and drive disconnect built in with integral OCP?
Sent from your mom's iPhone. She says hi.
Jason
walkerj is online now   Reply With Quote
Old 08-23-2011, 10:08 PM   #4
To me that would meet code.. I've installed like that before.
Old 08-24-2011, 10:54 AM   #5
Ax grinder
raider1's Avatar
If the drive has an integral disconnecting means that would qualify as the required disconnect.
Chris
Old 08-24-2011, 12:31 PM   #6
Pretty good reason to use MCC buckets with drives built-in, or stick the drive in the bucket in place of the contactor.
Tags
controllers, disconnect, motors, vfd
No code heads in sight mcclary's electrical Off Topic 36 10-31-2010 10:16 PM
new to this sight lineman Introductions 19 10-20-2010 10:19 PM
PNP or NPN by sight alone? MDShunk PLCs, VFDs, Motors and Controls 17 06-23-2010 07:08 PM
ac disconnect RODDBODD NEC Code Forum 38 02-11-2009 09:38 PM
Disconnect or not?? Nosparxsse NEC Code Forum 34 01-24-2009 10:31 AM