Originally Posted by alselec53
Posted this question in General talk too.. hope that's ok.
Cannot find the code req for running 1/2" emt from a commercial (restaurant) building to a outside sitting area (gazebo). Its about 7 or 8 ft from where I would run power from the building to the wooden structure (large gazebo). Is this legal? how would I support the emt pipe? How high do I have to be? Is there a min or max distance I can run pipe in free air? The other option is chip out the cement and go underground. Also, do they make a outdoor ceiling fans made for wet conditions, direct rain? not patio cover fans. Havent come accross this in my 25+ years of elec work. Any info would help.
Thanks AL
358.30 Securing and Supporting. EMT shall be installed
as a complete system in accordance with 300.18 and shall
be securely fastened in place and supported in accordance
with 358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place at least every 3 m (10 ft). In addition, each EMT run
between termination points shall be securely fastened
within 900 mm (3 ft) of each outlet box, junction box, device
box, cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be
permitted to be increased to a distance of 1.5 m (5 ft) where
structural members do not readily permit fastening within
900 mm (3 ft).
Exception No. 2: For concealed work in finished buildings
or prefinished wall panels where such securing is impracticable,
unbroken lengths (without coupling) of EMT shall
be permitted to be fished.
(B) Supports. Horizontal runs of EMT supported by openings
through framing members at intervals not greater than
3 m (10 ft) and securely fastened within 900 mm (3 ft) of
termination points shall be permitted.