i dont know if this is true cuz i havent tested it. but a city of anaheim inspector, who was way on top of the code, told me theres no need for it in a one or two hour wall or ceiling cuz the box was UL tested without it.
brandoelectric is offline   Reply With Quote
Old 01-22-2007, 12:37 AM   #2
I actually think that might be true, but I can't confirm that. I seem to remember a max gap between the box and the gypsum, above which you had to use fire caulk or similar intumescent seal. The use of rated device boxes in fire rated assemblies is covered under the UL Orange Book, of which I do not own a copy. It's actually a 2 volume expensive affair. The NEC is mute on the matter.
Old 01-22-2007, 01:49 AM   #3
K&R
K&R's Avatar
I know in this are the only time I have had to worry about sealing is in the hospitals and restraunts. They want the boxes wraped, penitrations sealed, and boxes sealed between the drywall on every firewall. Most of them even spec the Hilti products.
K&R is offline   Reply With Quote
Old 02-02-2007, 07:55 PM   #4
I have seen it used on common walls in condos and aptments.
acrwc10 is offline   Reply With Quote
Old 02-03-2007, 07:37 AM   #5
Pierre Belarge's Avatar
Default Fire Resistance Penetrations
There seems to be a lot of confusion with the need for "fire caulking" and penetration sealing for fire resistive locations.
If one is talking about 1 & 2 family dwellings, there are very few locations in a dwelling that require fire caulk. Most dwellings will only require fire caulking where the garage is located adjacent to living space and the walls/ceilings of a boiler room. The rest of the locations in a dwelling are not listed as fire assemblies, therefore those locations will only require "draftstopping". Draftstopping can be performed in many different ways, and is a lot less expensive than firestopping.
Pierre Belarge is offline   Reply With Quote
'09 ICC code thekctermite General Electrical Discussion 0 10-20-2008 09:49 AM
wiring ?'s and code randypape NEC Code Forum 0 09-14-2008 05:49 PM
"Flame Spread Rating" of NM Cable??? sparkysteve Other Codes and Standards 8 03-12-2008 06:33 AM
National Electrical Code: Analysis & Explanation of the Underwriters' Electrical Code Joe Tedesco Vintage Electrical 3 12-28-2007 11:47 PM
Code book vs. Code book "Handbook" shotdown General Electrical Discussion 14 09-10-2007 12:39 PM