05-17-2011, 03:36 PM
flammable storage locker grounding
Does the NEC require those yellow, steel flammable storage lockers to be grounded or bonded to the electrical systems grounding system?
05-17-2011, 03:44 PM
NEC, Nope. NFPA and OSHA do.....
Don't release the magic smoke!
05-17-2011, 03:47 PM
Can you cite the rules that require the storage cabinet to be bonded?
05-17-2011, 04:00 PM
05-17-2011, 04:15 PM
N.ational E.lectrical C.ode or NFPA 70 is concerned with the installation, maintenance, and repair of ELECTRICAL equipment and devices. A metal hazmat storage locker is not by definition ELECTRICAL. NFPA has cognizance for electrical safety as a function of fire safety but has other instructions for hazmat/hazwaste. NFPA 30, flamable and combustable liquids code. Osha has cog on workplace safety standards. 1910.106 covers flam storage.
05-17-2011, 04:26 PM
I looked up OSHA 1910.106 and the only thing it says about grounding is that class I liquids' dispensers and containers must be eletrically connected when filling
05-17-2011, 04:30 PM
Yeah, I looked again and didn't see much REQUIRING grounds. I know every Co. I ever worked for including Govt. required storage lockers, wast collection drums, etc.. to be grounded. Op asked if NEC required it. Nope. They don't give a dang about flam lockers....
05-17-2011, 04:31 PM
Oh, wait, you is the OP!!!!
So... it looks like the answer is NO. However, if I am storing and working with class I liquids I need to interconnect the dispenser and container when filling. If I am doing this action in the vicinity of the storage locker I can, for convenience sake, connect the locker to a ground and then use the locker as a grounding point for the filling operation.
05-17-2011, 04:36 PM
Sounds good to me. Hand pump, electric pump???
05-17-2011, 04:39 PM
Generally, in our flam storage/handling area, we have a copper braid run along the wall. The lockers and such, get a pigtail hardwired to that and hand pumps, drums, etc. get a gator jaw clamp to the braid. braid is terminated with a #6 to a ground rod driven thought the slab into grade.
05-17-2011, 07:14 PM
Sometimes in a flammable marked cabinet you may have a charge build up due to static. All cabinets probably should be connected and then to earth as best you can. Most people know about the possible buildup of electrons when sliding a gasoline can across the bed of a pickup... especially if it is a plastic bed. The same is true in a cabinet. It is all about an environment free of potential difference that could cause an arcing situation.
05-18-2011, 06:35 AM
There is no reason to bond or ground the cabinet. Static is not an issue with closed containers. The only time static is a real issue is when you are transferring flammable liquids from one container to another. In that case you need to bond the two containers together.
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
tool storage
MarcDuke |
32 |
02-04-2011 11:11 PM |
Nec 2011 locker rooms gfci
brother |
0 |
11-03-2010 12:29 PM |
Storage in Truck
jculber |
21 |
10-16-2010 08:03 AM |
compartment storage
vos |
35 |
10-13-2010 04:47 PM |
UK: storage heaters
philip657 |
UK Electrical Forum |
4 |
12-31-2009 12:15 AM |