While reading through Article 410 I was suprised to read the following rule:
410.24 Connection of Electric-Discharge Luminaire.
(A) Independent of the Outlet Box. Electric-discharge luminaires supported independently of the outlet box shall be connected to the branch circuit through metal raceway, nonmetallic raceway, Type MC cable, Type AC cable, Type MI cable, nonmetallic sheathed cable, or by flexible cord as permitted in 410.62(B) or 410.62(C).
My boss always let us just knock out the big KO (3-4") on the back of fluorescent surface mount fixtures, mount the hole over the ceiling box, and bring the individual conductors down into the fixture.
Am I correct in understanding this does not meet code based on the above?
Thanks
josh5879 is offline   Reply With Quote
Old 02-15-2010, 03:22 PM   #2
child please.....
NolaTigaBait's Avatar
Rewards Points: 14
I do the same thing. It's ok as long as you can access the taps without remvoing the fixture. I think that article is more for the chain hung fixtures and the like.
Old 02-15-2010, 03:34 PM   #3
Rewards Points: 5,198
Default flourescent fixture
Yes, that is correct.
Old 02-15-2010, 04:17 PM   #4
josh5879's Avatar
Rewards Points: 77
Yeah, you guys must be right about the intent of the code, I'm just bothered that the fact of the matter is that the actual text is technicly talking about all types of fixtures, including surface mounted.
Old 02-15-2010, 04:49 PM   #5
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 1,556
Josh-
Read the Entire article section not just the first part.
410.24 (B)- Access to Boxes- Electric-Discharge Luminaires surface mounted over concealed outlet,pull or junction boxes and designed not to be supported solely by the outlet boxe shall be provided with suitable openings in the back of the luminaire to provide access to the wiring in the box
So your boss is correct in the way he tells you to do it.
Keep in mind that you must read the entire section of a code article. You can't stop when you think you have the answer. You need to read the entire code section and reference those articles that are referred to in the original code section
Old 02-15-2010, 04:56 PM   #6
Default Flourescent
Originally Posted by manchestersparky View Post
Josh-
In the orignial post, is just knocking out the large KO in the back of the fixture satisfy the code as far as Approved for the Purpose?
Old 02-15-2010, 05:13 PM   #7
Rewards Points: 250
If the fixture is mounted over a junction box the large KO must be removed to allow access to the JB. Just passing the circuit conductors thru a 1/2" KO from the JB will not cut it.
Jim Port is offline   Reply With Quote
Old 02-15-2010, 05:20 PM   #8
Rewards Points: 250
Default cut
I used to pop the 1/2 ko out then use sheet metal cutters and expose the whole box. Most guys I knew did the above. It just makes it harder for the next guy.
Mike Guile is offline   Reply With Quote
Old 02-15-2010, 07:02 PM   #9
What I used to do was to take out the 1/2 ko then use a knockout cutter to cut a larger hole.
The hole must be large enough to allow access to all the wiring in the box behind the fixture.
Old 02-16-2010, 02:58 AM   #10
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,114
You guys who knock out the KO and mount it over a box, do you use a snap in bushing?
~Matt
I HAVE THE RIGHT TO OFFEND ANYONE I PLEASE. YOU HAVE THE RIGHT TO BE OFFENDED, YOU DO NOT HAVE THE RIGHT TO SHUT ME UP.
Old 02-16-2010, 03:09 AM   #11
I saw a guy do it once.
SparkYZ's Avatar
Rewards Points: 506
When I mount a strip light over a 3/o or 4/o box, I usually use a holesaw and cut a big hole so it is accessible. If I cheat and just use a KO (sometimes I dont have the time), I like to use a conduit connector for a smooth edge.
SparkYZ is offline   Reply With Quote
Old 02-16-2010, 04:36 AM   #12
Rewards Points: 508
~Matt
Romex connector
Wireless is offline   Reply With Quote
Old 02-16-2010, 06:00 AM   #13
josh5879's Avatar
Rewards Points: 77
Josh-
These two rules are talking about two completly different things:
410.24(B) has nothing to do with the isssue of the wiring method to the fixture, it concerns one thing: allowing access to the wiring in the outlet box, it doesn't say you can go ahead and wire the fixture directly from the conductors in that outlet box.
410.24(A) does talk about the wiring to the fixture, and it only lists a couple of specific methods metal raceway, NM raceway, MC, AC, MI, NM, or flexible cord. It doesn't seem to allow individual conductors from an outlet box.
Old 02-16-2010, 10:38 AM   #14
child please.....
Rewards Points: 14
You are way over-thinking this.
Old 02-16-2010, 10:50 AM   #15
Rewards Points: 2,050
Josh, I agree you are over-thinking it.
Just slap the damn fixture up over the box once you punch out the big KOs that allow box access. That is all the code requires.
Old 02-16-2010, 11:12 AM   #16
child please.....
Rewards Points: 14
If the Badger ok's the install, you are good to go
Old 02-16-2010, 11:15 AM   #17
Rewards Points: 250
Originally Posted by Wireless View Post
Romex connector
I've always used a 7/8" rubber bushing. But they are saying that you need to knock it out to a large size so I don't know of any bushings that big. I wonder if my 1 3/8" Unibit would be considered big enough for access to the box?
JackBoot is offline   Reply With Quote
Old 02-16-2010, 11:43 AM   #18
You need to use a fully dressed malleable steel 4" chase nipple
Old 02-16-2010, 12:20 PM   #19
JayH's Avatar
http://www.asihome.com/ASIshop/index...ath=40_172_232
Upping my post count one mistake at a time!
JayH is offline   Reply With Quote
Old 02-16-2010, 12:50 PM   #20
Rewards Points: 1,170
And 4" chase locknut with 4" chase bushing.
ralpha494 is offline   Reply With Quote
Another fluorescent fixture question BuzzKill General Electrical Discussion 10 02-11-2010 01:06 PM
fluorescent lights artisanelec Lighting Design 21 10-08-2009 12:19 AM
fluorescent ballasts BuzzKill General Electrical Discussion 11 04-28-2009 02:48 AM
Fluorescent Lighting jerryd General Electrical Discussion 4 11-11-2007 07:50 PM
Troubleshooting bedroom outlet wiring? Operator4819 General Electrical Discussion 1 03-30-2007 06:58 PM