11-05-2009, 09:28 PM
#101
He's definitely a turd. Yes.
11-05-2009, 09:29 PM
#102
Terrorism is a naughty word.. let me be clear, I intend to be PC when ever it makes me look good
11-07-2009, 05:12 AM
#103
Originally Posted by electures
If you disagree with this, please provide code sections to back it up.
Enjoy your day!!
I disagree, the fused disconnect at the unit is not the final branch circuit
OCPD, it is overload protection, no change in circuit wiring is needed. I'll
provide as many code sections as you do.
Frank, Arizona,USA
It's what you learn after you know it all that counts
11-08-2009, 02:37 PM
#104
Inspector
You are incorrect.
Article 100 Definitions which states;
Branch Circuit, Individual.
A branch circuit that supplies only one utilization equipment. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
The conductors from the fused/breakered disconnect to the AC unit are the Individual Branch-Circuit conductors. The fuse or breaker in the disconnect is the final branch-circuit overcurrent device and the breaker in the panel is the feeder protection.
If a non-fused/breakered disconnect is installed then the breaker in the panel is the final branch-circuit overcurrent device.
Hope this clears things up for you.
Enjoy the rest of the weekend!
Kevin
11-09-2009, 10:02 PM
#105
You are incorrect.
Feeder.
Kevin
Article 210.2 shows you all the other articles that amend Article 210
"Branch Circuits".
Top of the list in Table 210.2 is Air Conditioning Equipment.
Article 440.6 , 440.31 , 440.32. Tell us that the nameplate on the equipment is used to determine the rating or ampacity of the Disc. Means,
the Branch Circuit Conductors, the Controller, the Branch Circuit SS/GF
Protection , and the Seperate Motor Overload Protection.
Article 440.52(A)(3) Protection Agianst Overload, (3) a fuse.
Example: MCA=20a MOP=35a fuse or hacr c.b.
35a c.b. , #14 thwn conductors , fused disconect w/25a fuses for o.l.
protection, #14 thwn conductors to equipment termination block.
EE spec like this every day of the week.
Frank, Arizona,USA
11-10-2009, 04:43 PM
#106
Inspector
"Branch Circuits".
I agree with everything stated about branch circuits. The confusion here is where does the branch circuit begin. If a fused/breakered disconnect is installed then the branch circuit begins @ the disconnect and everything stated above is correct plus the requirements of 440.35. If a non-fused/breakered disconnect is installed, the conductors from the disconnect back to the panel are still feeders by definition and the requirements of Article 215 apply including 215.1 and 215.3.
In the example above #14 thwn can be ran from the panel to the fused/breakered disconnect and then to the AC unit. MOP in the disconnect can be 25A, however, the feeder protective device cannot be set higher then 310.16 which is 20A. This installation may lead to nuisance tripping at the feeder protective device. As the inspector I can't require conductors larger than #14 THWN, but I will not except a feeder OC device larger than 20A (which is what the #14 THWN is rated at).
I did find 440.52(A)(1) interesting though. Is it stating that the fuse or ITCB cannot be set higher then 125% even though the nameplate allows higher?
As for EE's, just because they spec it doesn't make it compliant.
Interesting discussion. It's shame there are no other comments.
Kevin
11-10-2009, 05:42 PM
#107
Rat Bastard
bluh....
Reason: bluh...
11-10-2009, 11:44 PM
#108
Kevin,
Just so we are on the same page, The fused disco. at the ac unit is not
part of any manafactures instrutions, right, same page.
The only good code back-up I have is, If you believe that these are feeders, and they feed a (code) structure outside, then a GES must be
installed at the disco.
Now,IMO. If the purpose of the fused disco is to protect the ac unit, then
the wires on the line side of the disco are branch circuit conductors.
If the purpose of the fused disco is to protect the wires on the load side
of the disco, then the supply conductors are feeders.
I don't agree that the fused disco is installed to protect the line side
conductors to the disco, and I don't agree that the addition of the disco
changes the line side conductors from branch circuit to feeders.
Pizza just showed up, later.
Frank, Arizona,USA
11-11-2009, 10:11 PM
#109
Inspector
What, no code sections?
11-11-2009, 10:45 PM
#110
For post #108, Article 250.32(A)
I did not think that you would need this one !!
I guess all the EC's in your area are driving ground rods for their AC disco.
feeders ?
Frank, Arizona,USA
Reason: add info
11-16-2009, 05:58 PM
#111
Inspector
feeders ?
250.32 Buildings or Structures Supplied by a Feeder(s)
or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s) supplied
by feeder(s) or branch circuit(s) shall have a grounding
electrode or grounding electrode system installed in
accordance with Part III of Article 250. The grounding
electrode conductor(s) shall be connected in accordance
with 250.32(B) or (C). Where there is no existing grounding
electrode, the grounding electrode(s) required in 250.50
shall be installed.
Frank,
I think the key word here is building or structure. Neither of which apply here.
Kevin
11-17-2009, 10:38 PM
#112
Kevin,
NEC Definition of Structure:
"That which is built or constructed"
Making a concrete pad, supplying pipes and electrical power is that which
is built and constructed. There is no doubt that an outdoor air conditioner
compressor set-up is a 'structure'. A parking lot pole light is a structure,
the NEC even deleted the requirement for a disconnect on these. The NEC
says what it says' seperate structures supplied by feeders are required
to have a GES'.
Frank, Arizona,USA
11-18-2009, 05:57 AM
#113
Kevin,
to have a GES'.
Wow. You've really lost your marbles on that one if you think that an A/C is a seperate structure. Let's not confuse this already confusing topic anymore than it needs to be.
11-18-2009, 07:47 PM
#114
Floppy Member
Hey now, you keep your logic and common sense to yourself.
11-18-2009, 07:54 PM
#115
Yes, I'm sorry. I'll try to remember not to share any commonsense with any others.
11-18-2009, 09:34 PM
#116
This is not a 'logic or common sense' Forum, it is a NEC Forum, and as We
are required to use NEC defined words when used.
Structure is a NEC defined word: 'That which is built or constucted'.
You can not tell me that an outdoor AC compressor unit was not built or
constructed. Three different trades, concrete, hvac, and electrical, were
required to install this, these are construction trades, it is a structure.
Frank, Arizona,USA
11-19-2009, 11:02 PM
#117
Floppy Member
So a post light is a separate structure as well then?
Edit: Also, if you replace the concrete pad with a prefored plastic or concrete pad, have the electricians only mount the disconnect and wire their end, then a condenser could be installed by just an hvac contractor
Yesterday, 12:02 AM
#118
Yes, a post light is a seperate structure, it is not required to have a GES
because it is on a single branch circuit.
It does not matter 'who' installs 'what' the AC unit has been built or constructed.
The AC unit, like the post light, does not require a GES if it is on a single
branch circuit, But, if you are in the camp that feels by useing a fused
disconnect at the unit that it is being supplied by 'feeders', than you
must also alude to the fact that a GES is required at the disconnect.
Frank, Arizona,USA