Garbage Disposal and Dishwasher on same circuit. - Electrician Talk - Professional Electrical Contractors Forum
View Poll Results: Disposal and Dishwasher on the same circuit
Yes 43 62.32%
No 26 37.68%
Voters: 69. You may not vote on this poll
Old 08-19-2011, 05:16 PM   #1
Inspector
electures's Avatar
Rewards Points: 306
Default Garbage Disposal and Dishwasher on same circuit.
1/3 HP Disposal, 6.8 amps, 120V
Dishwasher 9.9 amps, 120V
Are they permitted on the same 20 amp circuit. I will reserve my thoughts for later.
PLEASE VOTE!!
electures is offline   Reply With Quote
Old 08-19-2011, 05:29 PM   #2
Fried Bologna um um good!
jwjrw's Avatar
No it's a violation because one motor pulls more than half the circuit.
Old 08-19-2011, 05:30 PM   #3
Inspector
electures's Avatar
Rewards Points: 306
Originally Posted by jwjrw View Post
No because one motor pulls more than half the circuit.
Did you vote?
Old 08-19-2011, 05:32 PM   #4
jwjrw's Avatar
Originally Posted by electures View Post
Did you vote?
Nope......
Old 08-19-2011, 05:36 PM   #5
Inspector
electures's Avatar
Rewards Points: 306
Nope......
Please vote. It is easier to keep track of. Thanks!!
Old 08-19-2011, 05:36 PM   #6
Rewards Points: 2,050
Default No/Yes
No / Yes
20 amp cir. NO
30 amp cir. YES
Old 08-19-2011, 05:38 PM   #7
Inspector
electures's Avatar
Rewards Points: 306
Originally Posted by Cletis View Post
No / Yes
20 amp cir. NO
30 amp cir. YES
Guess I should clarify what size circuit, Huh?
Old 08-19-2011, 05:40 PM   #8
Rewards Points: 2,000
210.23(a) (2)
Mr Rewire is offline   Reply With Quote
Old 08-19-2011, 05:42 PM   #9
Default humm
210.23(A)(2) 50% rule fastened in place 20 amp
Yes
Old 08-19-2011, 05:44 PM   #10
jwjrw's Avatar
Don't feed the troll.........
Old 08-19-2011, 05:59 PM   #11
Speedy Petey's Avatar
Rewards Points: 2,168
The 50% rule only applies if: "lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied."
This is not the case. No lighting is supplied, nor is any cord and plug non-fastened in place equipment.
If all equipment on the circuit is fastened in place the 50% rule does not apply.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
electricmanscott (08-19-2011), Josue (08-19-2011), user4818 (08-19-2011)
Old 08-19-2011, 06:00 PM   #12
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
Old 08-19-2011, 06:48 PM   #13
jwjrw's Avatar
I forgot all about that................
We always pull a 3 wire. One circuit for each.
Old 08-19-2011, 06:49 PM   #14
Ax grinder
raider1's Avatar
Rewards Points: 1,080
I agree with Petey.
Chris
Old 08-19-2011, 06:49 PM   #15
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
25 amp ocpd.
Old 08-19-2011, 07:38 PM   #16
Rewards Points: 2,002
I've put them both on a single 15 amp circuit before. I prefer to put them both on one 20 or 2 15's, but I don't have the slightest issue with one 15 amp circuit for both.
Old 08-19-2011, 07:52 PM   #17
Bababoee
captkirk's Avatar
Rewards Points: 2,030
mine isnt usually on for more than a couple of seconds. For some reason I ran two 20's under my sink but its total overkill . I usually just put one 20 for both.
Full time Bovine Scatologist.
Old 08-19-2011, 07:56 PM   #18
I would feel a little uncomfortable if the load was 16.7amps on a 15amp breaker w/ 14 wire. It would probably only reach that level for a few seconds a day on avg but over the years it could cause problems and it's way over 80%.
I would feel better w/ 2 15 amp circuits. I will say it's been a few years since I wired a house. If ya ran 2 15 amp circuits is there anything else you could hit w/ one of them? Lights...nah, fridge...nah.
I'd go 2-15 amp circuits but 1 would probably never give ya problems...probably.
I remember them being seperate when I was doing houses.
cultch is offline   Reply With Quote
Old 08-19-2011, 07:59 PM   #19
BIGRED's Avatar
Rewards Points: 1,006
I remember when I first started, the disposal and the light over the sink on one circuit.
You pay peanuts, you get monkey's!
BIGRED is offline   Reply With Quote
Old 08-19-2011, 08:02 PM   #20
Now in THIS example the disp cannot be more than 50%.
disposal of... BuzzKill General Electrical Discussion 12 07-19-2011 03:59 PM
garbage disposal spider General Electrical Discussion 3 05-20-2011 05:48 PM
Dishwasher cord daverk87 NEC Code Forum 25 04-18-2011 10:29 AM
garbage drill bits Josue Tools, Equipment and New Products 30 01-01-2011 01:39 PM
garbage disposal dwaincyrus General Electrical Discussion 4 03-23-2008 06:41 PM