This is my first pool hook up, my understanding is that a hard wired pump motor does not have to have a gfci breaker, is this correct? The guy we are wiring it for wants the gfci breaker anyway, i just wanted to be sure.
rebel34 is offline   Reply With Quote
Old 03-26-2008, 10:52 PM   #2
"A" inside wireman
randomkiller's Avatar
Not sure about other type of installs (resi) but all the spec jobs I have wired have had the pool house sub panel fed from a GFCI breaker.
"One Nation Under God"
Old 03-27-2008, 07:01 AM   #3
Up until the 2008 NEC you are correct. This was changed for 2008.
Most of us used a GFI anyway.
Actually I can't remember the last hardwired pump I did. We are a seasonal climate and pumps are usually removed for winter. Hardwiring doesn't work for that.
Old 03-27-2008, 07:19 AM   #4
"A" inside wireman
I haven't ever done a pump that wasn't in a filter house or similar building. Most have been done in conduit with a small flex whip to the motor.
Old 03-27-2008, 09:35 AM   #5
Yet when wired for 220 cord & plug, no GFCI was needed.
Old 03-27-2008, 10:11 AM   #6
The 2005 NEC added a change requiring GFI protection for 240v pumps as well.
Old 03-27-2008, 06:52 PM   #7
As per 2005NEC, only a receptacle needs GFI. If hardwired, no GFI required. Seems so silly that we need to go crazy w/ bonding and grid, but a GFI is not required.
A light IS required to be GFI protected.
I need to buy the 2008 NEC book. NJ is still doing 2005.
heel600 is offline   Reply With Quote
Old 03-28-2008, 07:15 AM   #8
680.22(B) 0f the 2008 code says GFIC protection is required for both cord and plug and direct connected swimming pool pump motors.
guschash is offline   Reply With Quote
Protecting NM subelect NEC Code Forum 91 11-02-2008 12:43 PM
120 vs. 240 pool pump wirenut1110 General Electrical Discussion 15 06-21-2008 08:56 AM
GFCI on 3 phase remote fountain pump george nicholson NEC Code Forum 1 05-21-2008 09:09 PM
GFCI in pool house Sparks 1942 NEC Code Forum 7 04-24-2008 06:10 PM
I Need HELP finding a well pump???? please mikewardjr General Electrical Discussion 10 10-05-2007 06:39 PM
Electrician Talk © 2006 - 2010 The Building Network LLC