I have a large panel. I notice a number of grounds and neutrals are sharing the same connection under the screw on the bus bar. What I mean is that there is ONE ground and ONE neutral under the same screw. I was told this is not acceptable and neutral should always get a separate screw and grounds can be combined under the same screw. Is this true?
J V is offline   Reply With Quote
Old 05-15-2017, 01:22 PM   #2
Rewards Points: 8
Not sure what the codes are where you are? But in California the code is one screw one wire.
Burgis is offline   Reply With Quote
Old 05-15-2017, 01:29 PM   #3
RePhase277's Avatar
Rewards Points: 4,126
Read the label on the panel cover, it will tell you what combinations of wires are acceptable for that panel.
Old 05-15-2017, 05:21 PM   #4
NRA Member
backstay's Avatar
Rewards Points: 1,438
Electricians of a certain age always did it that way. If it's 40 plus years old and hasn't failed, I don't mess with it.
frenchelectrican and Majewski like this.
backstay is online now   Reply With Quote
Old 05-15-2017, 06:03 PM   #5
Rewards Points: 1,304
All it depending if this is a main panel or subpanel that is a whole different set of game to play.,,
but with resdentail panel .,, yes it is common to see that but again as RePhase277 mention very clear .,, check the panel for latest details due many panel have different specs.,,
plus some local customs in there in the mix. so expect that.
However majorty of commercal and industrails panels ., no .,, only one wire per screw ( unless stated in prints or other approved means )
Old 05-15-2017, 10:16 PM   #6
cabletie's Avatar
Rewards Points: 102
408.41 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Old 05-17-2017, 06:41 PM   #7
Rewards Points: 674
Up here in Canada you can't have neuts and grounds on the same termination strip let alone under the same screw.
Sparky9868 likes this.
Any friend of anemone is a friend of mine
ELECTRICK2 is offline   Reply With Quote
Old 05-23-2017, 01:11 PM   #8
So, where are you bonding ground and nuetral?
Sent from my XT1254 using Tapatalk
cl2sparky is online now   Reply With Quote
Old 05-23-2017, 01:40 PM   #9
Watt Pusher
B-Nabs's Avatar
Rewards Points: 438
The neutral bar in the main panel is bonded to the can by way of a strap or special screw or the like. Then branch neutrals land individually on the neutral bar, and grounds land on the ground bar. The ground bar can have more than one under each screw.
Sent from the unmarked van outside HackWork's house.
ELECTRICK2 and PlugsAndLights like this.
Old 05-23-2017, 01:40 PM   #10
Click Here
Rewards Points: 1,512
Their main disconnect is in a separately enclosed section of the panel. I believe inside of that section is where the neutral and ground are bonded. On the outside of that internal enclosure the branch circuit breaker section is now like a subpanel, in which the neutrals and grounds stay separate.
Old 05-23-2017, 01:42 PM   #11
Thank you. Seems like an awful waste on money, though.
JMHO
Old 05-23-2017, 01:55 PM   #12
"That Guy"
cuba_pete's Avatar
Rewards Points: 1,801
Where did you discern that? I didn't see it in the thread.
At any node in an electrical circuit, the sum of currents flowing into that node is equal to the sum of currents flowing out of that node...Ground Rods Need Not Apply
Old 05-23-2017, 03:08 PM   #13
Click Here
Other threads.
Old 05-23-2017, 03:14 PM   #14
"That Guy"
cuba_pete's Avatar
Other threads.
Ah...
How do you ground a panel? 99cents Canadian Electrical Code Forum 24 01-29-2017 10:11 PM
Single Phase 120 Neutral to Ground reads 52 volts? comicbookmechanic Industrial Electrical Forum 13 12-30-2016 04:14 PM