10-06-2009, 09:57 PM
#21
B4T Scotchkote installer
Originally Posted by william1978
You can't use the building steel as you GEC. I don't know what the inspector was talking about when he said it had to be run with other conductors. Was he talking about equipment grounds?
No.. the water main was plastic.. why I wanted to use building steel
But, it turned out first 25' was copper inside the building, then changed to plastic
10-06-2009, 09:59 PM
#22
Licensed Pro
So did you use it as a GEC?
Vince Lombardi
10-06-2009, 10:08 PM
#23
Gec
As a fault current is increasing in a circuit the "the magnetic field" that is encompassing the "HOT" conductor actually increases the ampacity of the EGC so that it will trip the breaker quicker. Therefore it is always better to run the EGC as close to the circuit conductors as possible.
RIVETER
Reason: Brain fart
10-06-2009, 10:12 PM
#24
Yes.. I used the water pipe
I will post some pics and start a new thread in the next few days .. did the job last year and I still "don't get it"
10-06-2009, 10:20 PM
#25
Licensed Pro
Well... if you "don't get it" you should be an inspector.
Vince Lombardi
10-06-2009, 10:21 PM
#26
#27
Service grounding
I have not looked at the code book for a while so I may be wrong.Let me know what you think. The picture of the grounding system showed the "GROUNDING" conductor tied to the neutral buss, then to the water pipe system and then to the system grounding electrode. As I remember, the grounding conductor connected to the panel must be connected to the metal water pipe system, if the system has one, and to the system ground rod. (Both are electrodes and should be independent of each other.) The picture depicted the system grounding conductor depending solely on the integrity of the water pipe system; If for some reason the metal water system is replaced with rubber, or plastic in the future, which does happen, the integrity of the system grounding is compromised.
10-06-2009, 10:35 PM
#28
GEC or not
I tried to edit my post but could not, so I will retract part of what I said in an earlier post. I mispoke; I meant to say that the equipment ground, not the GEC, should be run close to the circuit conductors to facilitate the overload device.
RIVETER (Egg on face)
Reason: Mispelling and too many BUDs
10-07-2009, 03:02 AM
#29
Which is why the connection is required to be in the first 5' of the pipe entering the dwelling, that portion is less likely to be replaced with a different piping system.
Rick Boudreau
Tal Afar, Iraq
10-07-2009, 03:04 AM
#30
That's not very nice!
Rick Boudreau
Tal Afar, Iraq
10-07-2009, 07:17 PM
#31
Licensed Pro
Were just joking around there are plenty of good EI's.
Vince Lombardi
10-08-2009, 12:36 AM
#32
I know......I actually agree with you for the most part, I have seen some really good inspectors in my time, and I have seen some really bad ones as well.
I try and stay in that first group!
Rick Boudreau
Tal Afar, Iraq
10-08-2009, 01:56 AM
#33
grounding
This is a good diagram. However, I would like it more if it considered the effect of a lightning stike on the service entrance conductors. I believe it would be better to connect the neutral bus or meter directly to a close ground rod to form the lowest inductance path. The way it is shown here, the lightning current will travel through the whole above-ground water pipe on its way to earth. This will cause extreme potential differences throughout the building. Not a good situation.
EJPHI
10-08-2009, 08:30 AM
#34
EJPHI
For some reason everyone seems to feel that it needs to be next to the main breaker. And im refering to the ground rods.... By code you allowed to go at the meter or even the service drop. ...Good luck trying to pass that way though...
10-08-2009, 12:25 PM
#35
Licensed Pro
EJPHI
I agree with your assessment. But in certain situations the ground rods go wherever they can be driven. Code says what the Code says.
Vince Lombardi
10-08-2009, 07:01 PM
#36
Mad Skills
EJPHI
You do realize that many times the steel skeleton of a building is used as the path for the lighting strike ...and what is attached to the skeleton.....everything ~ plumbing, electric, sprinklers, etc.
10-08-2009, 07:19 PM
#37
Grounding electrodes
It does not matter if you have 100 steel beams anchored five feet in reinforced concrete,you must bond them and still place a supplemental ground rod at the service.
RIVETER
10-09-2009, 05:14 AM
#38
It does not matter if you have 100 steel beams anchored five feet in reinforced concrete,you must bond them a nd still place a supplemental ground rod at the service.
RIVETER
Where is that requirement in 250.52(A)(2)?
The only electrode that requires a supplemental electrode is a metal underground water pipe, and it does not have to be a ground rod - 250.53(D)
John from Baltimore
"One day at a Time"
10-09-2009, 08:49 PM
#39
Supplemental ground rod
Prove what I have said is wrong and I will defend it.
RIVETER
10-09-2009, 08:51 PM
#40
Not Peter D
He just did.
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
2 ground rods
MikeD |
NEC Code Forum |
116 |
12-07-2009 12:38 PM |
Ground rods
charlie Bob |
25 |
08-25-2009 06:16 PM |
Ground rods
BIGRED |
NEC Code Forum |
39 |
07-20-2009 10:40 PM |
Ground Rods
Dude Man |
14 |
04-08-2009 01:38 PM |
Connecting two ground rods
sharkmobil |
Services and Service Equipment |
22 |
03-11-2008 11:16 PM |