Old 04-13-2009, 03:20 PM   #1
Default grounding vs bonding?????
I just get confused at times ,when& where&how each is used.Can someone please give me a brief explanation and example of each. Thanx in advance
stillirnin is offline   Reply With Quote
Old 04-13-2009, 04:33 PM   #2
I am too lazy to explain but try this article. Also do a search from that page for
Grounding vs Bonding Part 2 of 12.
You will have to go to the second page of the search results . You will see 12 articles on this subject
Alice
Old 04-13-2009, 05:56 PM   #3
Chris Kennedy's Avatar
That means she has no idea.
Bulldozers and Dirt
Old 04-13-2009, 08:54 PM   #4
redbeard43's Avatar
grounding is from the electrode to the can
bonding is from the neutral to the ground
ungrounded conductor is the hot
grounded conductor is the neutral
bond bushings go to the ground bar to bond the conduit coming from underground or flex, sometimes even the ground wire protection conduit
You have the ring, and I see that your schwarz is as big as mine.May the schwartz be with you!
redbeard43 is offline   Reply With Quote
Old 04-13-2009, 08:59 PM   #5
s.kelly's Avatar
If you really want to look at the subject, probably the best book on this imho is Soares book on grounding. Fairly easy to read and not fall asleep, but full of lots of good info!
s.kelly is offline   Reply With Quote
Old 04-14-2009, 09:11 AM   #6
lectricboy's Avatar
A grounded conductor isn't always a neutral, ie; three phase corner ground.
http://ecatalog.squared.com/pubs/Ele...2700DB0202.pdf
lectricboy is offline   Reply With Quote
Old 04-14-2009, 04:15 PM   #7
I am too lazy to explain...
I do have an idea.
Grounding is when you have your shoes off and you are standing on wet earth.
Bonding is when you have 2 people and their lips are touching.
Alice
Old 04-14-2009, 07:37 PM   #8
Licensed Pro
Magnettica's Avatar
Maybe start here...
250.4 General Requirements for Grounding and Bonding.
The following general requirements identify what grounding
and bonding of electrical systems are required to accomplish.
The prescriptive methods contained in Article 250 shall be
followed to comply with the performance requirements of this
section.
(A) Grounded Systems.
(1) Electrical System Grounding. Electrical systems that
are grounded shall be connected to earth in a manner that
will limit the voltage imposed by lightning, line surges, or
unintentional contact with higher-voltage lines and that will
stabilize the voltage to earth during normal operation.
(2) Grounding of Electrical Equipment. Non–current-
carrying conductive materials enclosing electrical conduc-
tors or equipment, or forming part of such equipment, shall
be connected to earth so as to limit the voltage to ground on
these materials.
(3) Bonding of Electrical Equipment. Non–current-carrying
conductive materials enclosing electrical conductors or equip-
ment, or forming part of such equipment, shall be connected
together and to the electrical supply source in a manner that
establishes an effective ground-fault current path.
(4) Bonding of Electrically Conductive Materials and
Other Equipment. Electrically conductive materials that
are likely to become energized shall be connected together
and to the electrical supply source in a manner that estab-
(5) Effective Ground-Fault Current Path. Electrical
equipment and wiring and other electrically conductive ma-
terial likely to become energized shall be installed in a
manner that creates a permanent, low-impedance circuit
facilitating the operation of the overcurrent device or
ground detector for high-impedance grounded systems. It
shall be capable of safely carrying the maximum ground-
fault current likely to be imposed on it from any point on
the wiring system where a ground fault may occur to the
electrical supply source. The earth shall not be considered
as an effective ground-fault current path.
Vince Lombardi
Old 04-15-2009, 06:29 AM   #9
eddy current's Avatar
I do have an idea.
Exactly
Old 04-18-2009, 02:18 PM   #10
I do have an idea.
I loved that response from electrista also.
3phase is offline   Reply With Quote
Old 04-18-2009, 05:23 PM   #11
Unlimited Lic.Electrician
william1978's Avatar
I do have an idea.
Old 04-18-2009, 08:58 PM   #12
I do have an idea.
When two people fall to the ground with their lips touching it is called Earthing
user5941 is offline   Reply With Quote
grounding and bonding george nicholson General Electrical Discussion 1 01-29-2010 10:51 AM
vehicle mounted generator bonding and grounding SparkyInCanadaEh General Electrical Discussion 16 10-10-2009 09:13 AM
NEC 250.32 Grounding/Bonding Issue Lightning NEC Code Forum 23 07-06-2008 11:01 PM
grounding & bonding question bigredc222 Services and Service Equipment 35 02-29-2008 07:00 PM
Grounding and bonding a transformer Jim Workplace Safety 5 08-18-2007 08:08 PM