Old 11-02-2009, 07:47 PM   #1
Unlimited Lic.Electrician
william1978's Avatar
Default Having a brain fart.
Where is it in the code book where I can find what the smallest wire I can tap on a 50amp lighting cir? I will be using soow to feed 50 amp track light and the cord will be somewhere between 4' to 6' long.
Old 11-02-2009, 07:51 PM   #2
Licensed Pro
Magnettica's Avatar
Likely in article 400, cords.
Or maybe 240.21.
Vince Lombardi
Old 11-02-2009, 07:54 PM   #3
Thats what I was thinking also. I bet I have looked thru art.400 about 3 times I must be missing it. I am going to look again.
Old 11-02-2009, 07:59 PM   #4
Licensed Pro
Magnettica's Avatar
I'm also looking in 210 right now for at least until the Yankees start beating up the Phillies again.
Vince Lombardi
Old 11-02-2009, 08:02 PM   #5
Licensed Pro
Magnettica's Avatar
Wait a second... a 50 amp track light?
Try 210.19 (A)(4) Exception No. 1
Vince Lombardi
Old 11-02-2009, 08:03 PM   #6
I'm looking at 240.5(B)(2) not a 100% sure if it applys to my case.
Old 11-02-2009, 08:04 PM   #7
Licensed Pro
Magnettica's Avatar
And I think you're right.
Vince Lombardi
Old 11-02-2009, 08:05 PM   #8
B4T Scotchkote installer
Black4Truck's Avatar
All the Halo Tracs I have seen are 20a max.
What brand are you using?
Old 11-02-2009, 08:16 PM   #9
Not sure of the brand I will look tomorrow and let you know, but it is 50amp track. I have track light that will cover about 50,000 sq.ft. of a museum. The drawings call for #4 on a 50amp cir, but the electrical engineer let us back it down to #6 on a 50amp cir.
Old 11-02-2009, 09:19 PM   #10
It sounds doable, but since 240.5 B,2 references fixture wire, I believe you would have to use one of the wire types listed in 402.3 for it to apply.
If the tracks have end feeds, I’m not sure if those wires would qualify as "fixture wires", since those are more for branch circuit wire connection… although, 402.5 does allow fixture wires to be used as branch circuit wires as permitted elsewhere in the code.
Maybe run it by your local inspector to see what he thinks.
402.12 does reference 240.5 for overcurrent protection, so it looks like you can tap a 50A branch circuit with a #12 or larger fixture wire, but the actual allowable ampacity for the #12 fixture wire is limited to 23 Amps and likewise #10 fixture wire would have an allowable ampacity of 28 Amps, according to Table 402.5.
Another random brain fact s.kelly Off Topic 13 10-12-2009 09:14 PM