Old 10-05-2009, 05:13 PM   #21
B4T Scotchkote installer
Black4Truck's Avatar
Originally Posted by GEORGE D View Post
what about 334.80?
334.80 tells you to use 60 degree column on 310.15
Only problem is there is no chart titled 310.15
I asked the Forum Historian (Ken.. AKA TOOL) and he directed me to 310.16
Could it be the CMP screwed up and gave us wrong information
Old 10-05-2009, 05:54 PM   #22
The 90 degree column is for bundling only. You won't find any terminals rated higher than 75 degrees so you can't put anything bigger than an 90 amp breaker in with 4-3.
chris856 is offline   Reply With Quote
Old 10-05-2009, 05:55 PM   #23
Not Peter D
Romex is totally dangerous and should be permanently banned as a wiring method.
Old 10-05-2009, 06:06 PM   #24
Unlimited Lic.Electrician
william1978's Avatar
Wait a minute romex is your bread and butter right?
Old 10-05-2009, 06:17 PM   #25
child please.....
NolaTigaBait's Avatar
Where are you getting 90 amps?....Its either the 60 degree chart or 310.15b6. I think it is ok to use 4-3nm under the 310.15b6 chart(it is accepted here). Yes, I know they are not thhn, i've heard people say that it was.
Old 10-05-2009, 06:19 PM   #26
I read it as 70 amp breaker max for 4/3 NM
THAT really sucks!!!!
Old 10-05-2009, 06:32 PM   #27
Seen your member
Peter deosn't use romex, he uses SO and lamp cord.
Old 10-05-2009, 06:33 PM   #28
Not Peter D
I stopped using that too. I now use telephone wire and Cat 5 for everything.
Old 10-05-2009, 06:35 PM   #29
Anyone hear of a "ser" cable that is like NM, but service entrance rated and would allow #4 to be put on 100 amp breaker
Old 10-05-2009, 06:57 PM   #30
child please.....
I thought you use ser and seu on the 60 degree column as well. I think nm or ser is ok to use as a feeder.
Old 10-05-2009, 07:02 PM   #31
#4 SE works for 100 amp, but the 4/wire cable is the problem for sub panels
Why I was interested in the "SER" rated cable
Table 310.15(B)(6) Conductor Types and Sizes for
120/240-Volt, 3-Wire, Single-Phase Dwelling Services and
Feeders. Conductor Types RHH, RHW, RHW-2, THHN,
THHW, THW, THW-2, THWN, THWN-2, XHHW,
XHHW-2, SE, USE, USE-2
Old 10-05-2009, 07:08 PM   #32
child please.....
I would think that SER would fall into that category.
Old 10-05-2009, 07:10 PM   #33
Professional Nit Picker
There's no reference to ampacity for NM in the 60's. The word 'ampacity' wasn't used in the NM Section until 336-26 of the 1999.
The word ampacity is used in the 1987 NEC section 326-26
" conductors shall be rated at 90 degree ( 194 F). The ampacity of types NM and NMC cable shall be that of 60 degree( 140 F) conductors and shall comply with section 310-15."
The 1987 is the oldest NEC I have at home.
(# 6 NM Cable is rated for 55 amp at 60 degree in the '87)
Old 10-05-2009, 09:35 PM   #34
Seen your member
I guess I was looking for a specific paragraph titled Ampacity.
The language you mention began in the 1975.
Old 10-05-2009, 10:44 PM   #35
JohnJ0906's Avatar
You can derate from the 90 degree column. However, the final result cannot exceed the 60 degree column. See 334.80.
4-3 CU romex is a 70 amp conductor, regardless if the terminal is rated 75 deg or 60.
John from Baltimore
"One day at a Time"
Old 10-22-2009, 01:22 PM   #36
Inspector
electures's Avatar
Default Yes, it is permissible.
I presented this question to my first & fourth year h/s electrical class. They agree that 6/3 NM cable used as a feeder can be protected by a 60A breaker provided the calculated load does not exceed 55A's.
Penn-Tech all day!!
electures is offline   Reply With Quote
What to use when stripping romex? Gents Tools, Equipment and New Products 46 12-20-2008 08:44 PM
Mc Or Romex Or Bx Nitro9119 General Electrical Discussion 3 05-19-2008 08:48 PM
romex/conduit 2leggedogwbrassballs General Electrical Discussion 44 02-17-2008 02:36 PM
White 12/2 romex BIGRED General Electrical Discussion 10 07-30-2007 08:31 PM
Romex Where Not To Use BILL General Electrical Discussion 3 03-11-2007 09:53 AM