I have an existing 1 inch conduit that is ran underground. Can I run speaker wires and a 3 # 12 wires for a 120 VAC 20 amp circuit in the same conduit? and if I can what type of speaker wire should I install.
Thanks
AMPED is offline   Reply With Quote
Old 02-22-2013, 06:09 PM   #2
Rewards Points: 516
What you need to be worried about here is the voltage rating of all wire insulation involved. Don't know if you can find legit speaker wire around here with the higher rating.
As a design stand point I also don't think it's a good idea. I would imagine there would be a lot of noise/distortion imposed on the speaker system.
running dummy is offline   Reply With Quote
Old 02-22-2013, 06:34 PM   #3
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 402
no, except under very specific circumstances (I am assuming the speakers are powered by a class 2 power source). read 725 starting here:
725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors, and Medium-Power Network-Powered Broadband
Communi- cations Cables.
(A) General. Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any
cable, cable tray, com- partment, enclosure, manhole, outlet box, device box, race- way, or similar
fitting with conductors of electric light, power, Class 1, non–power-limited fire alarm circuits,
and medium-power network-powered broadband communica-
tions circuits unless permitted by 725.136(B) through (I).
The Following 2 Users Say Thank You to wildleg For This Useful Post:
Big John (02-24-2013), hardworkingstiff (02-24-2013)
Old 02-22-2013, 07:04 PM   #4
Rewards Points: 87
My initial responce to the customer wanting the bid was no I cannot do it. Then I was informed that the two competing electrical companies assured him it could be done. They would just have to install a speaker wire with a heavier insulation.
Old 02-24-2013, 12:25 AM   #5
Rewards Points: 38
It is a very bad idea to do this, and probably not per code. Bad idea, as there will be a tremendous amount of noise on the speakers. I wouldn't do it and explain why in my bid. If the home owner cares about the install and not just the $$$, we will not use the other contractors.
If you look at the exceptions to 725.54 if they control wires and are associated with the high voltage (120v) devices and controls, you are able to as long as the rating on the low voltage cable jacket meets the conditions below, you can.
725-54 Does does not address speaker wires.
725-54. Installation of Conductors and Equipment
(a) Separation from Electric Light, Power, Class 1, Nonpower-Limited Fire Alarm Circuit Conductors, and Medium Power Network-Powered Broadband Communications Cables.
(1) In Cables, Compartments, Cable Trays, Enclosures, Manholes, Outlet Boxes, Device Boxes, and Raceways. Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, nonpower-limited fire alarm circuits, and medium power network-powered broadband communications cables.
Exception No. 1: Where the conductors of the electric light, power, Class 1, nonpower-limited fire alarm, and medium power network-powered broadband communications circuits are separated by a barrier from the Class 2 and Class 3 circuits. In enclosures, Class 2 or Class 3 circuits shall be permitted to be installed in a raceway within the enclosure to separate them from Class 1, electric light, power, nonpower-limited fire alarm, and medium power network-powered broadband communications circuits.
Exception No. 2: Conductors in compartments, enclosures, device boxes, outlet boxes, or similar fittings, where electric light, power, Class 1, nonpower-limited fire alarm, and medium power network-powered broadband communications circuit conductors are introduced solely to connect to the equipment connected to Class 2 or Class 3 circuits to which the other conductors are connected, and
a. The electric light, power, Class 1, nonpower-limited fire alarm, and medium power network-powered broadband communications circuit conductors are routed to maintain a minimum of 0.25 in. (6.35 mm) separation from the conductors and cables of Class 2 and Class 3 circuits, or
b. The circuit conductors operate at 150 volts or less to ground and also comply with one of the following:
1. The Class 2 and Class 3 circuits are installed using Type CL3, CL3R, or CL3P or permitted substitute cables, provided these Class 3 cable conductors extending beyond the jacket are separated by a minimum of 0.25 in. (6.35 mm) or by a nonconductive sleeve or nonconductive barrier from all other conductors,
westcojack is offline   Reply With Quote
Old 02-24-2013, 02:49 AM   #6
Rewards Points: 1,000
Can someone please explain why they believe that speaker wire has to say the words "speaker wire" on it?
uconduit is offline   Reply With Quote
Old 02-24-2013, 05:43 AM   #7
wildleg's Avatar
Rewards Points: 402
who is they ?
Old 02-24-2013, 05:51 AM   #8
Originally Posted by wildleg View Post
who is they ?
Whom ever
Old 02-24-2013, 07:06 AM   #9
Rewards Points: 356
Speaker wire is generally a class II wiring but I think the insulation is rated 300V. Would I do it-- no ...Is it legal -- perhaps. The question is if the speakers are from a class II source.
Old 02-24-2013, 08:14 AM   #10
Rewards Points: 12,320
Can you do it, yes. Will it work OK, possibly (shielded cable grounded at one end might keep the AC noise out of the speaker).
Will it be code compliant? Doubtful. As others have said, most of the time speakers are not supplied by a Class 1 power supply. Conductors from Class 2 & 3 power supplies are not allowed to be installed in a conduit with power conductors.
I have done it before and gotten away with it. I don't do it know.
Giving up on unbiased truth.
Old 02-24-2013, 09:10 AM   #11
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 1,598
According to 725.130(A) exception No. 2- you could reclassify the class 2 circuit to a class 1 circuit. That will allow you to install it in the same conduit.
Basically your using class 1 wiring methods on a class 2 power source. Then calling it a class 1 ciruit.
Now class 1 speaker wire ? doubtful. Another class 1 type of cable that is class 1 rated ? Possible
Good idea ? - NO
Legal - Yes as long as you do everything that is in the exception
Anything Worth Doing ....
Is Worth Doing Right
Old 02-24-2013, 10:27 AM   #12
wildleg's Avatar
Rewards Points: 402
Good idea ? - NO
if you are going to make it a class 1 wiring system, the power source must be reidentified as a class 1 power source (if it is identified as a Class 2 then that marking must be changed/re-labeled). 725.130 A ->725.124
Old 02-24-2013, 10:35 AM   #13
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 262
Even re-classifying it as Class 1 is not a free pass. It still needs to be "functionally associated" when pulled in the same raceway. I know I've stretched that definition to the breaking point myself, but it'd be a hard fight claiming that the speakers and lighting were associated wiring.
Old 02-24-2013, 01:53 PM   #14
Thumbs down
Yes -thats why I stated you need to follow all the items in the exception
High voltage and low voltage seperation Stu424 Canadian Electrical Code Forum 3 06-07-2012 11:15 PM
minimum depth of burried low voltage and high voltage canada lortech NEC Code Forum 4 05-11-2012 08:05 PM
Low voltage & High voltage in same conduit HW&Electric General Electrical Discussion 12 06-11-2011 08:25 AM
Typical low voltage guy asking high voltage question. LARMGUY General Electrical Discussion 13 09-02-2010 12:59 AM
high voltage/ low voltage separation mosquito General Electrical Discussion 4 07-08-2010 04:56 AM