Old 04-20-2011, 07:32 PM   #1
jewalker88's Avatar
Default Micro/rangehood circuit
My local AHJ stated that 110v outlet for gas range can't come off of the micro/range hood cir. I can't find a code to suport that. anyone have any Ideals?
jewalker88 is offline   Reply With Quote
Old 04-20-2011, 07:34 PM   #2
Chief Electron Relocator
Why not ask the AHJ?
Old 04-20-2011, 07:47 PM   #3
It could be article 422.16(B)(4)exception(5)
Old 04-20-2011, 07:52 PM   #4
NRA Member
backstay's Avatar
That is my prefered method. I put a 50 amp range receptacle in and a 110 volt duplex that I then feed to the micro/fan. You didn't feed the gas range from the SABC, did you? You can, but can't then feed the micro/fan from it. 210.52(B)(2)exc 2
Old 04-20-2011, 07:56 PM   #5
NRA Member
backstay's Avatar
Damm, I will have to change my ways. I guess the gas range outlet is coming off the SABC from now on.
Old 04-20-2011, 08:00 PM   #6
I did the same thing for years. I have never been caught on it but it could be a reason for a red tag. I thought about writing an exception to that section for a gas range receptacle.
Old 04-20-2011, 08:06 PM   #7
NRA Member
backstay's Avatar
I already run 2-20 amp SABC to the kitchen, 1-20 amp to the dinning room and 1-20 amp for the range/mico/fan. It would seem better to run the three together instead of taking the range off the SABC. JMO
Old 04-20-2011, 08:08 PM   #8
jewalker88's Avatar
no had dedicated circuit for the micro/fan and gas cooktop
Old 04-20-2011, 08:10 PM   #9
jewalker88's Avatar
i can see where that could be it thanks
Old 04-20-2011, 08:11 PM   #10
jewalker88's Avatar
that is exactly how i always do it just had one AHJ call me on it
Old 04-20-2011, 09:13 PM   #11
rexowner's Avatar
That would be a good exception, that makes a lot of sense.
I used to do it too without realizing there was a problem, until
a coworker "caught" me doing it. Looked it up, and sure enough.
rexowner is offline   Reply With Quote
Old 04-20-2011, 09:26 PM   #12
Thing is that the micro is over 50% of the branch circuit rating for cord connected appliance so can't share that circuit with lighting and receptacles. If I remember right..
Old 04-20-2011, 10:23 PM   #13
That is correct but the exception would have to allow it.
Some have argued that a microwave range hood is listed as a microwave so technically it would not fall under this article. However, I know the inspector who wrote this rule and his reasoning was microwave range hoods.
Old 04-21-2011, 10:20 AM   #14
Ax grinder
raider1's Avatar
Actually most are listed as both a microwave and a rangehood because they must meet both listings if the microwave also serves as a rangehood.
Chris
Old 04-21-2011, 02:06 PM   #15
Chris
I thought Bob actually dug up some info a year or so ago stating that they were listed as microwaves. I never bought into it but thought it worth mentioning.
Old 04-21-2011, 03:27 PM   #16
Ax grinder
raider1's Avatar
The one that I looked at had a listing as both a microwave and a rangehood.
Chris
Old 04-21-2011, 05:44 PM   #17
Which exception?
Old 04-21-2011, 05:46 PM   #18
NRA Member
backstay's Avatar
Post #6, Dennis was talking about writing one.
Old 04-21-2011, 05:51 PM   #19
I think 210.23(B)(2) is fairly clear. It makes sense to me that you don't want to have over 50% of a circuit that is shared being utilized by one appliance.
Old 04-21-2011, 06:02 PM   #20
NRA Member
backstay's Avatar
The issue is how much the range would add to that circuit. If the micro was on the counter, we could wire the gas range receptacle, fridge receptacle, plug the micro in and what ever else on the same SABC. This exception would make more sense.
Color Code On USB micro??? leestover General Electrical Discussion 4 01-16-2011 04:39 PM
6 Drops per 15 A circuit/8 Drops per 20 A circuit. Whats your opinion? romexrocket NEC Code Forum 32 06-11-2010 06:38 AM
Micro & Island outlet BIGRED General Electrical Discussion 62 03-12-2010 10:13 AM
FYI For SeeSnake Micro Owners KayJay Tools, Equipment and New Products 49 08-04-2009 07:38 AM
240 vs 120 circuit ?????? tlg7mm General Electrical Discussion 4 12-16-2008 06:42 AM