A dwelling unit has 5 cooking appliances:

9 kw
10 kw
14 kw
16 kw
24 kw

What is line load calculation.

Using note 2 of table 220.55 I came up with 24k

My instructor is telling me that it is 23.6k

I think he is wrong. Is he?
EvilBunny is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 02-26-2009, 04:48 PM   #2
Senior Member
 
Join Date: Jan 2009
Location: NC
Posts: 601
Default

Quote:
Originally Posted by EvilBunny View Post
A dwelling unit has 5 cooking appliances:

9 kw
10 kw
14 kw
16 kw
24 kw

What is line load calculation.

Using note 2 of table 220.55 I came up with 24k

My instructor is telling me that it is 23.6k

I think he is wrong. Is he?
Well I tend to agree with you but I really suck at these. How did he get 23.6. Seems like he missed the part where the first two ranges must be 12Kw but I still can't get 23.6.
electricista is offline   Reply With Quote
Old 02-26-2009, 06:08 PM   #3
Registered Member
 
Join Date: Apr 2008
Location: Minneapolis
Posts: 37
Default

I came up with with 24KW

12+12+14+16+24=78

78/5=15.6

15.6-12=3.6 rounds up to 4

4*.05=.2

5 ranges in col. C=20KW

20*1.2=24

I don't see how he could have come up with 23.6... make him show his work.

I found it...

He did not round for the major fraction...

15.6-12=3.6

3.6*.05=.18

20*1.18=23.6

Last edited by collin.thomas; 02-26-2009 at 06:12 PM.
collin.thomas is offline   Reply With Quote
Old 02-26-2009, 07:02 PM   #4
Junior Member
 
EvilBunny's Avatar
 
Join Date: Feb 2009
Location: Maine
Posts: 16
Default

NEC 2008 Table 220.55 Note 2 states:

Quote:
...Then the maximum demand in Column C shall be increased 5 percent for each kilowatt or major fraction thereof by which this average value exceeds 12kW.
The "major fraction thereof" is where the point of contention is. I guess the interpretation is that since it doesn't say "round up" then it means that you just take 5% of whatever is left over after the 12kW?

I'm not sure what else it could be.

Is there a place in the code where we're told that a "major fraction" means to round up?
EvilBunny is offline   Reply With Quote
Old 02-26-2009, 07:27 PM   #5
Registered Member
 
Join Date: Apr 2008
Location: Minneapolis
Posts: 37
Default

Well the way my instructor explained it is:
5 percent for each kilowatt 5 percent for each major fraction (being .5 or more)

not

5 percent for each kilowatt5 percent of each major fraction

If your were supposed to take 5% of the fraction, why would it state major fraction.
collin.thomas is offline   Reply With Quote
Old 02-26-2009, 07:36 PM   #6
Junior Member
 
EvilBunny's Avatar
 
Join Date: Feb 2009
Location: Maine
Posts: 16
Default

Agreed.

This is obviously the way it's supposed to be calculated. 24k has to be right.

Thanks.
EvilBunny is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Multiple Pipe Bending tc7447 General Electrical Discussion 11 01-12-2008 03:11 PM
Link multiple switches smallman General Electrical Discussion 6 12-21-2007 05:16 PM
how do you hang multiple lights? shotdown General Electrical Discussion 11 08-04-2007 10:14 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 04:52 AM.


Electrician Talk © 2006 - 2009 The Building Network LLC

Search Engine Optimization by vBSEO 3.2.0