Old 11-01-2009, 10:27 PM   #41
I am a RAT.
william1978's Avatar
Are you on a code making panel Bob?
Old 11-02-2009, 12:20 PM   #42
Originally Posted by Joe71 View Post
As I read the 2008 code:
1) Now "all" receptacles in a dwelling must be "tamper resistant".
2) This even applies to GFCI receptacles. (Isn't the GFCI a "tamper resistant" receptacle by definition?!)
3) An exception is the ceiling mounted receptacle for a garage door.
The code seems to allow an exception for ceiling mounted receptacles for such things as fluorescent lights, smoke detectors, etc. Is this correct?
4) All breakers must be of the "arc sensing" type. This even though some panels at my jobber (and home depot/Lowes) come with a few of the non-arc sensing breakers installed. Why is this discrepancy?
5) My jobber says that the GFCI breakers ARE NOT "arc sensing". Are they an exception to the rule or are GFCI arc sensing breakers just not available as yet?
Thanks.
While 210.12 B has some very weak wording "or similar rooms or areas" which an inspector might get caught up on, my understanding is that Kitchen, laundry, bathroom, garage, unfinished basement and outdoor circuits are excluded from AFCI requirement. A local inspector also allows exceptions for circuits with low voltage lighting due to nuisance tripping issues.
ElectricBill is offline   Reply With Quote
Old 11-02-2009, 05:08 PM   #43
Is it worth it if it saves just one human life? No.
How about if that one life was yours?
I Conduit is offline   Reply With Quote
Old 11-02-2009, 05:28 PM   #44
Floppy Member
Unless the washing machine was in a closet.
De-ja-vu
idontknow is offline   Reply With Quote
Old 11-02-2009, 06:07 PM   #45
Ratus Maximumus
Bob Badger's Avatar
No .... I am just a code geek with too much time on his hands.
The NFPA web site sucks but with some searching you can find all kinds of stuff, the entire 2011 NEC draft copy is here.
http://www.nfpa.org/assets/files/PDF...0-ROPDraft.pdf
You can also find the ROPs (Report on Proposals) and ROCs (Report on Changes) for the 2002, 2005, 2008 and 2011 NEC online.
In those boring pages you find out the real reasons why the rules where changed and see who is asking for the changes.
Bob Badger
Electrical Construction and Maintenance
MA, RI, CT
Old 11-02-2009, 08:02 PM   #46
I am a RAT.
Thanks, cool link.
Old 11-02-2009, 08:04 PM   #47
I am a RAT.
I think he would still argue with the cost of the rec. that just saved his life.
DC and receptacles Golden Arc General Electrical Discussion 7 04-03-2009 07:16 PM
Load Calc. for Old Single Family Dwellings Reseman Services and Service Equipment 5 05-31-2008 10:21 AM
Article 725 - CL2x vs. CL2 vs. CL2R in Dwellings BillS NEC Code Forum 2 03-14-2008 10:23 AM
Childproof Receptacles Nosparxsse NEC Code Forum 13 01-26-2008 10:44 AM
Electrical in existing dwellings MDShunk Other Codes and Standards 3 01-11-2008 09:54 PM