07-28-2009, 12:34 PM
electrorick
neutral size rule
Where in the code do I justify the size of the neutral being smaller than the hots in a service
I know why I just can't find the rule
Rick
I know you understand
what you thought I said
but what you heard
is not what I meant
07-28-2009, 12:59 PM
Ax grinder
Take a look at 230.42(C) and 220.61.
Chris
07-28-2009, 05:28 PM
How about 250.24(C)(1)
07-28-2009, 07:59 PM
Ax grinder
That section is referenced by 230.42.
Chris
07-28-2009, 08:42 PM
Rat Bastard
Does anyone even use this rule?...I always just wire the neutral the same size as the ungrounded conductors. I guess on a huge commercial job with thousands of feet of wire maybe?
07-28-2009, 08:46 PM
I have the option of buying SEU with the smaller neutral. I often do.
-Marc, ABC, XYZ, PhD, 1-2-3
07-28-2009, 08:50 PM
Rat Bastard
I wasn't aware they made it that way. What's the cost difference?
07-28-2009, 08:53 PM
about a nickel a foot.
07-28-2009, 08:55 PM
Rat Bastard
Serious?...That isn't much of a savings.
07-28-2009, 08:56 PM
If you have to carry the roll of it from the store to the truck, you might appreciate the savings in an entirely new way.
07-28-2009, 08:58 PM
Rat Bastard
Good point. I had to run a 70 feet of 4/0 ser feeder in a fishing camp 16 feet off the ground the other day. A few less pounds would have been nice.
07-28-2009, 09:34 PM
I often install 400 amp services with 2- 200amp panels outdoors that have feed thru lugs. I then pipe to the inside panels sometimes 50- 75 feet away with 3/0 copper and a 1/0 grounded conductor.
If the calculated load was small enough I could actually go down to a #2 in each panel but I never have done that.
07-28-2009, 09:41 PM
Often times the neutral size is a spec'd size. Seems like most of the jobs I do spec full size neutrals.
07-28-2009, 09:47 PM
I don't doubt it but I bet you do commercial work and not resi work where the neutral is spec'd.
07-29-2009, 03:38 PM
electrorick
wire price diff
I went to get feeders for 200amp panel
3/0 3/0 1/0 copper was $9.00 a foot x 20' = $180.00
4/0 4/0 2/0 al was 2.50 a foot x 20'= $ 50.00
the 4/0 4/0 2/0 was on the roll already together
and of course I'm comparing copper to al price not 3/0 vs 1/0 price
Rick
but what you heard
is not what I meant
07-29-2009, 03:42 PM
electrorick
so what size ground do you use on those?
I am doing one like that now
this in ref to Dennis and his 400 amp service feeding two panels
but what you heard
is not what I meant
Reason: get the question to proper person
07-29-2009, 05:56 PM
Your EGC is determined by 250.122 and what size OCPD you have. In my case a #6 is all that is needed to each panel, but I often pull #4 simply because I stock that size.
07-30-2009, 11:56 PM
#18
Doing a job for a hospital now and each MRI room calls for one ground and an isolated ground, each to be the same size as hots. For what it's worth, in Chicago neutral must be same size as ungrounded conductors in services up to 400 amps.
07-31-2009, 10:16 AM
#19
I've been on jobs where they oversize the neutral and call it a super neutral.
08-01-2009, 12:50 PM
#20
I've seen a lot of jobs lately that they spec a larger (or even doubled up) neutral for feeders.
 Don't fight .. Play nice!