Originally Posted by mcclary's electrical
4/0 SE/ SER cannot be used for a non dwelling 200 amp. 310.16 must be used.
230.42(A) General. The ampacity of the service-entrance conductors before the application of any adjustment or correction factors shall not be less than either (A)(1) or (A)(2). Loads shall be determined in accordance with Part III. IV, or V of article 220, as applicable. Ampacity shall be determined from 310.15. The maximum allowable current of busways shall be that value for which the busawy has been listed or labeled.
(1) The sum of the noncontinuous loads plus 125% of the continuous loads.
(2) The sum of the noncontinuous loads plus the continuous load if the service-entrance conductors terminate in an overcurrent device where both the overcurrent devcie and its assembly are listed for operation at 100% of their rating.
230.79. Rating of Service Disconnecting Means. The sevice disconnecting means shall have a rating not less that the
calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable.
240.4(B) Devices rated 800 Amperes or Less. The next higher standard overcurrent device rating
(above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors protected are not part of a multioutlet branch circuit...,
(2)
The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjuctments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
If you disagree with this, please provide the code section(s)...