NM-B and UF Cable in PVC conduit - Electrician Talk - Professional Electrical Contractors Forum
Old 12-23-2009, 02:06 PM   #1
Rewards Points: 153
Default NM-B and UF Cable in PVC conduit
Can anyone provide code references (other than 334.15B) about the installation of NM-B and UF cables in PVC conduits??
czars is offline   Reply With Quote
Old 12-23-2009, 02:28 PM   #2
Rewards Points: 2,002
Off the top of my head without looking it up:
NM-B cable is not permitted in any wet location including aboveground and underground raceways.
UF-B cable is permitted in any outdoor raceways, minding conduit fill of course. In fact, you can bury non-electrical tubing like plumbing PVC and then run UF cable in it, as the tubing is only a sleeve, not a raceway.
Old 12-23-2009, 02:55 PM   #3
Rewards Points: 464
What are you looking for. It is allowed but if it is a complete raceway then cable fill must be considered.
Old 12-23-2009, 04:47 PM   #4
Rewards Points: 153
Default NM-B and UF in conduit
Sometimes it's desireable to run NM-B or UF in conduit for protection.
UF is OK underground, but I feel better is it's in conduit to help deflect shovels, etc. A run of UF outside to an A.C compressor is better protected if it's in flex conduit. Running NM-B up garage walls and into attics protects the NM-B, but that's covered by 334.15B. for NM-B, I guess the real questions is it OK to run NM-B or UF in a properly sized conduit (considering derating for CCCs) between junction boxes, in a dry environment for cosmetic reasons?
Old 12-23-2009, 04:54 PM   #5
Ax grinder
raider1's Avatar
Rewards Points: 1,080
Yes.
Chris
Old 12-23-2009, 05:07 PM   #6
I own stock in FotoMat!
Rewards Points: 6,520
I think we should wait for the resident expert on UF and PVC............
Old 12-23-2009, 05:27 PM   #7
Ax grinder
raider1's Avatar
Your right, my bad.
I will take my Scotchkote and leave.
Chris
Old 01-15-2010, 08:42 PM   #8
Inspector/Electrician
codeone's Avatar
Rewards Points: 250
Article 334 NM Cable
334.15 Exposed Work. In exposed work, except as provided
in 300.11(A), cable shall be installed as specified in
334.15(A) through (C).
(A) To Follow Surface. Cable shall closely follow the surface
of the building finish or of running boards.
(B) Protection from Physical Damage. Cable shall be
protected from physical damage where necessary by rigid·
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC conduit, or other approved
means. Where passing through a floor, the cable shall be
enclosed in rigid metal conduit, intermediate metal conduit,
electrical metallic tubing, Schedule 80 PVC conduit, or
other approved means extending at least 150 mm (6 in.)
above the floor
Article 340 UF Cable
340.10
Uses Permitted. Type UF cable shall be permitted
as follows:
(1)
For use underground, including direct burial in the
earth. For underground requirements, see 300.5.
(2) As single-conductor cables. Where installed as singleconductor
cables, all conductors of the feeder grounded
conductor or branch circuit, including the grounded
conductor and equipment grounding conductor, if any,
shall be installed in accordance with 300.3.
(3) For wiring in wet, dry, or corrosive locations under the
recognized wiring methods of this
Code.
(4) Installed as nonmetallic-sheathed cable. Where so installed,
the installation and conductor requirements
shall comply with Parts II and III of Article 334 and
shall be of the multiconductor type.
codeone is offline   Reply With Quote
Old 01-19-2010, 11:28 AM   #9
Ax grinder
raider1's Avatar
above the floor
340.10
as follows:
(1)
Code.
Are you saying that UF cable installed inside of a dwelling unit underground in a PVC conduit is not permitted?
Chris
Old 01-19-2010, 11:43 AM   #10
codeone's Avatar
Rewards Points: 250
Chris
[/left]
No thats not what im saying. NM cable is not allowed!
Old 01-19-2010, 11:56 AM   #11
codeone's Avatar
Rewards Points: 250
300.5 Underground! Installations.
(C) Underground Cables Under Buildings.
Underground
cable installed under a building shall be in a raceway.
Old 01-19-2010, 12:33 PM   #12
Ax grinder
raider1's Avatar
Agreed, that was established early on in this thread.
Chris
Old 01-29-2010, 06:59 AM   #13
DGFVT
John's Avatar
Rewards Points: 168
How would you size a sleeve for Multiconductor Type USE cable, besides what the a POCO requires?
If will fit...put the cable in it?
R.E.D.
Old 01-29-2010, 09:33 AM   #14
Note 5, Chapter 9.
Old 01-29-2010, 10:47 AM   #15
DGFVT
John's Avatar
Rewards Points: 168
POCO mandated rules, see table.
Attachment 2587
R.E.D.
Old 01-29-2010, 10:55 AM   #16
But only for 'Vermont Utilities" customers.
Old 01-29-2010, 05:41 PM   #17
drsparky's Avatar
Rewards Points: 418
Good luck on pulling UF though conduit. Very stiff to work with.
Old 10-12-2012, 01:32 PM   #18
Default UF as an aerial
I have a temporary situation where I will be using UF for the undergound but I need to go from underground to overhead over a drive way and then back undergound and didnt want to break the wire? Any suggestions? can i use UF and use a messenger wire and strap it to that?
sokoservices is offline   Reply With Quote
Old 10-12-2012, 03:51 PM   #19
Rewards Points: 464
Yes, 340.10(3) and 396.10 plus T. 396.10(A)
NM-B cable run inside 2" conduit partimer31 NEC Code Forum 12 09-19-2009 03:59 PM
Conduit for UPS bman4523 Code Violation Discussion 7 02-05-2009 12:08 PM
ice in conduit te12co2w General Electrical Discussion 34 01-23-2009 09:47 PM
PVC MC cable in pvc conduit under slab? nealla General Electrical Discussion 17 09-09-2008 03:27 PM