07-30-2008, 06:22 PM
NM cable in EMT outside?
I understand that NM cable in EMT where it emerges from the house and goes to the outside panel is no longer acceptable. Can anyone tell me where the code says this is not allowed?
07-30-2008, 06:36 PM
Ax grinder
Take a look a this section:
334.12 Uses Not Permitted.
(B) Types NM and NMS. Types NM and NMS cables shall not be used under the following conditions or in the following locations:
(4) In wet or damp locations
Also take a look at this:
300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.8(C).
300.9 is new to the 2008 NEC.
Chris
07-30-2008, 06:52 PM
Finally! A 2008 change I agree with.
07-30-2008, 06:54 PM
Ax grinder
I agree as well. The 2005 alluded to this being a violation but really didn't come right out and say it.
Chris
07-30-2008, 07:08 PM
I don't like it because if the EMT with compression fittings is installed properly it should be dry inside, right? It also makes for another set of joints which is never as good of an installation.
07-30-2008, 07:31 PM
no... it wont be.
07-30-2008, 07:33 PM
"A" inside wireman
When have you seen a length of conduit outside that is really dry inside? The tell tale sign it has had water in it is that white powder and scale inside. I agree this is a change that was needed.
"One Nation Under God"
08-08-2008, 09:56 AM
Yesterday, actually. I think it depends on the part of the country you're in. Here in Colorado, the annual rainfall is about 12 inches (high desert), I've never experienced water in an above ground conduit but I have seen signs of it. Here, the humidity averages about 15% so it dries out pretty fast.
Also, what type of wires are in Romex? It doesn't say on the wires or the jacket?
08-08-2008, 07:12 PM
"A" inside wireman
Because the wires on thier own are not rated to be used that way. They are only rated as a unit (cable form).
08-13-2008, 11:23 AM
If it's under an eave, wouldn't it be a damp location?
Where does damp stop and wet begin?
Is a gutter a raceway?
08-13-2008, 11:46 AM
I don't know but the other code I don't care for is requiring "in-use" covers for all outdoor receptacles even for covered patios where it's just not necessary.
08-13-2008, 12:08 PM
Ax grinder
Basically the deliniation between a wet location and a dry location outdoors would be the exposure to weather.
Here is the definitions of wet and damp locations:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.
Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
Yes, here is the definition of a raceway:
Raceway. An enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or busbars, with additional functions as permitted in this Code. Raceways include, but are not limited to, rigid metal conduit, rigid nonmetallic conduit, intermediate metal conduit, liquidtight flexible conduit, flexible metallic tubing, flexible metal conduit, electrical nonmetallic tubing, electrical metallic tubing, underfloor raceways, cellular concrete floor raceways, cellular metal floor raceways, surface raceways, wireways, and busways.
Chris
08-13-2008, 12:10 PM
Ax grinder
406.8(B)(1) only applys to receptacles installed in a wet location. Receptacles installed under covered patios, depending on where they are located might be in a damp location.
Chris
08-13-2008, 10:10 PM
Whoops, wrong spot! Sorry.
08-14-2008, 11:38 PM
Put UF in that EMT.
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
Se Cable
JO SMYYT |
9 |
05-24-2008 09:15 AM |
Oily MC cable
Speedy Petey |
18 |
04-28-2008 05:56 PM |
Different Sized Cable
truth |
UK Electrical Forum |
3 |
02-14-2008 12:18 PM |
Cable Sizes
Sparky |
8 |
09-23-2007 03:54 PM |