Old 08-12-2010, 07:37 PM   #1
Default Outdoor Hot Tub
From my understanding you need a disconnecting means at least 5 foot away but within sight 680.12. Which means my disconnecting means could be as far as 50' away"within sight" correct? But how far is the receptacle need to be 6' to 20' away 680.22 (A)(3) or not less then 6' and not exceeding 10' 680.43 (A) ? Im thinking the 6' to 20' because the other may be implying indoor installation only.
Gamit is offline   Reply With Quote
Old 08-13-2010, 11:55 AM   #2
Introyble's Avatar
Always been my understanding and OSHA/Local Inspector interpretation, line of sight no matter what the conditions or 5' away.
I burn wire for beer money
Introyble is online now   Reply With Quote
Old 08-13-2010, 12:47 PM   #3
PGW Professional
Magnettica's Avatar
If you read 680.40 it tells you that hot tubs shall comply with the provisions of Parts I and II of article 680. So since you have an outside hot tub the required receptacle shall be located not more than 20' and not less than 6' from the edge of the tub. If it were an indoor tub than the receptacle would between the 6' and 10' area.
The Following User Says Thank You to Magnettica For This Useful Post:
frenchelectrican (08-14-2010)