Old 06-13-2012, 09:54 PM   #1
Default Pool wiring
I am wiring an in ground pool. It's going to have a heat pump that draws a heavy load so I'm going to put in a sub panel outside to serve the pool equipment.
I am arguing with a friend who is an electrician about the feeders to the sub panel. He claims that the feeders have to carry an insulated copper ground according to art. 250. My contention is that it has to be insulated and based on 250 but I can run aluminum.
Who is right?
________________________________
How can you have any pudding if you dont eat your meat
BurtiElectric is offline   Reply With Quote
Old 06-13-2012, 09:56 PM   #2
976-EVIL
mcclary's electrical's Avatar
Who is right?
you're right
BurtiElectric (06-13-2012)
Old 06-13-2012, 09:58 PM   #3
Originally Posted by mcclary's electrical
you're right
I read 680 like 3 times, and couldn't find. He swore up and down its in there
Old 06-13-2012, 10:00 PM   #4
You are right, but in the presence of corrosive pool chemicals, copper will stand up better than aluminum.
The Following 2 Users Say Thank You to InPhase277 For This Useful Post:
BurtiElectric (06-13-2012), Magnettica (06-13-2012)
Old 06-13-2012, 10:05 PM   #5
976-EVIL
I'm sure he thinks this applies:
(B) Equipment Grounding.
The flexible cord shall have a
copper equipment grounding conductor sized in accordance
with 250.122 but not smaller than 12 AWG. The cord shall
terminate in a grounding-type attachment plug.
However, that's not for permanent pools.
Old 06-13-2012, 10:05 PM   #6
erics37's Avatar
Hardly. They'll both get wrecked. Look at this picture - see all the pale green wires sticking out of the top of the panel? Those are bare copper ground wires. This panel was located adjacent to a swimming pool.
The Following 2 Users Say Thank You to erics37 For This Useful Post:
BurtiElectric (06-13-2012), slickvic277 (06-19-2012)
Old 06-13-2012, 10:17 PM   #7
It can be AL or CU, but it must be insulated.
680.25
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
Old 06-13-2012, 10:26 PM   #8
Good point, I just had to replace lights in a swimming pool area at a hotel. The chlorine ate through te sprinkler pipes that were in the ceiling 20 feet above the pool. You should have seen these pipes. There was nothing left!!!
Old 06-13-2012, 10:30 PM   #9
But notice that those wires are in fact only green and not eaten clean through. Aluminum feeders I have replaced near pools have crumbled into white dust.
Old 06-13-2012, 10:48 PM   #10
erics37's Avatar
Yeah without a doubt, the aluminum was in much worse shape at this place too.
The Following User Says Thank You to erics37 For This Useful Post:
PVC Depth for swimming pool wiring Magnettica NEC Code Forum 79 06-27-2012 09:14 PM
Above ground pool wiring Tony Saraceni General Electrical Discussion 4 05-25-2012 03:43 PM
Pool wiring ethics Salvatoreg02 NEC Code Forum 21 04-20-2012 06:49 AM
Pool wiring Gamit Residential Electrical Forum 7 04-23-2010 11:34 AM
Associated pool wiring underground wiring Magnettica Residential Electrical Forum 3 09-07-2009 04:08 AM