I'm studying to get my license and need help with one of my test questions/answers
One cooktop and two ovens are connected to one branch circuit in a kitchen of a one family dwelling. The cooktop has a nameplate rating of 4kw at 240v, while each oven has a nameplate rating of 5.5kw at 240v. The minimum load calculation for this branch circuit is ______ watts.
Range calculation: N.E.C 220.55??-image-834953987.jpg
I don't understand how they made this equation.
I appreciate the help.
Chas3x
Chas3x is offline   Reply With Quote
Old 09-05-2012, 01:29 AM   #2
A Little Short's Avatar
Rewards Points: 60
Attachment 16469
Chas3x
Look at note 4 of Table 220.55. That is for branch circuit load.
Edit: I just saw the answer sheet said to reference note 4. Do you understand how to use the table, and how to apply note 4?
The Following User Says Thank You to A Little Short For This Useful Post:
Chas3x (09-05-2012)
Old 09-05-2012, 02:48 AM   #3
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
Haven't done one of these in awhile...
3 appliances become (1) appliance.
Column C (1) appliance is 8,000 watts.
4kw + 5.5kw + 5.5 kw is 15kw.
15kw-8kw = 7kw
Add 5% for each additional kw over 8kw.
8kw x 35% = 10,800 watts
10.8 kw/ 240 = 45 amps.
That's off the top of my ahead I could be wrong.
Replies based on NEC 2014
The Following User Says Thank You to Magnettica For This Useful Post:
Chas3x (09-05-2012)
Old 09-05-2012, 07:31 AM   #4
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
When is it legal to run a full size range on #10s ? My last full time gig pulling wires at a Marriot residence inn had me doing that.
Old 09-05-2012, 09:36 AM   #5
Rewards Points: 60
15kw-8kw = 7kw
Wrong!
15kw-12kw= 3k
5% for each kw over 12kw
5% x 3kw=15%
8kw x 15%=1.2kw or 1200 w
8kw + 1.2kw = 9.2kw
or as the test wanted =9200W
The Following 4 Users Say Thank You to A Little Short For This Useful Post:
Chas3x (09-05-2012), I_get_shocked (09-05-2012), Magnettica (09-05-2012), mrxman (09-06-2012)
Old 09-05-2012, 03:13 PM   #6
Chas3x's Avatar
So you reduce the 15kw by the highest kw (12) in column C?
Old 09-05-2012, 03:21 PM   #7
Chas3x's Avatar
I just figured it out! I appreciate your help.
Old 09-05-2012, 08:24 PM   #8
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
Originally Posted by Little-Lectric View Post
Wrong!
15kw-12kw= 3k
5% x 3kw=15%
8kw + 1.2kw = 9.2kw
It's been awhile. I knew this like the back of my hand for the exam, but now not so much. I would have to check my Tom Henry books if I ever ran into this in the real world.
Thank you for correcting me.
Old 09-05-2012, 08:28 PM   #9
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
I don't like to make excuses for anything, but it was late and I had woken up from sleeping. I see now where I went wrong.
Notes:
1. Over 12 kW through 27 kW ranges all of same rating. For ranges individually rated more than 12 kW but not more than 27 kW, the maximum demand in Column C shall be increased 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual ranges exceeds 12 kW.
Celtic (09-05-2012)
Old 09-06-2012, 12:10 AM   #10
Rewards Points: 60
No problem, it was fun! I'm usually the one getting corrected!
Magnettica (09-06-2012)
Old 09-06-2012, 01:49 AM   #11
Wrong!
15kw-12kw= 3k
5% x 3kw=15%
8kw + 1.2kw = 9.2kw
Thanks for the info.
mrxman is offline   Reply With Quote
Old 09-07-2012, 09:42 AM   #12
Rewards Points: 25
[quote=Little-Lectric;801021
15kw-12kw= 3k
5% x 3kw=15%
8kw + 1.2kw = 9.2kw
or as the test wanted =9200W[/quote]
haha thats the way i learned it !!!!
irocin350 is offline   Reply With Quote
Dryer and Range BIGRED General Electrical Discussion 30 07-11-2010 02:15 AM
Gas Range Adaptor Conduit Phil General Electrical Discussion 24 06-20-2010 10:18 AM
Range circuit charlie Bob General Electrical Discussion 67 03-20-2010 11:43 PM
RF Switch with 200 ft. range azsparky General Electrical Discussion 2 12-05-2008 10:40 PM
Gas Range jelectric NEC Code Forum 3 03-09-2007 11:54 PM