Romex in conduit - Electrician Talk - Professional Electrical Contractors Forum
Old 01-19-2011, 11:43 PM   #1
Default Romex in conduit
I thought that the code said that romex is acceptable in conduit as long as it does not exceed 6'. Is this the case? I was called on this, saying that romex not allowed to be run in conduit in wet location. I ran romex through a piece of romex from the eve to a w/p gutter box through liquid tight conduit less than 6'. I have NEVER been called on this before.
eantonyg is offline   Reply With Quote
Old 01-20-2011, 12:09 AM   #2
kbsparky's Avatar
Rewards Points: 1,000
Conduit installed outdoors is considered a wet location. Even the inside of the conduit is a "wet" location.
Romex is not permissible in any wet locations.
-KB
The Following 4 Users Say Thank You to kbsparky For This Useful Post:
BBQ (06-05-2011), bruce6670 (02-12-2011), eantonyg (01-20-2011), Roger (06-10-2011)
Old 01-20-2011, 12:11 AM   #3
failelectric's Avatar
Rewards Points: 150
"Romex" is not rated to be in a wet location, even if it protected by a conduit. Consider yourself lucky for getting away with it before. UF cable is rated for wet locations, but has limitation on installation through buildings.
failelectric is offline   Reply With Quote
The Following User Says Thank You to failelectric For This Useful Post:
Old 01-20-2011, 12:16 AM   #4
Speedy Petey's Avatar
Rewards Points: 1,772
First off, welcome.
Forgive me if this comes off as rude, but I would think a "Certified Electrician <of> 17 years" would either know this, or have a code book and know exactly where to look for it.
Old 01-20-2011, 12:20 AM   #5
Conduit outside/underground is a wet location.. Romex is a no go in a wet location
randas is offline   Reply With Quote
Old 01-20-2011, 12:33 AM   #6
I own stock in FotoMat!
Rewards Points: 6,520
300.9 and 334.12(B)(4) are your Code references.
Old 01-20-2011, 12:37 AM   #7
Rewards Points: 150
Originally Posted by Speedy Petey View Post
First off, welcome.
I know many electricians that are great electricians that did not know this i would not fell bad about it.
The Following 2 Users Say Thank You to failelectric For This Useful Post:
eantonyg (01-20-2011), nitro71 (06-05-2011)
Old 01-20-2011, 12:38 AM   #8
RIP 1959-2015
HARRY304E's Avatar
Rewards Points: 1,344
Look at the 2011 NEC 300.9 and 334.12(B)(4)
And welcome to the forum let the fun begin
Old 01-20-2011, 12:39 AM   #9
RIP 1959-2015
HARRY304E's Avatar
Thanks Ken you beet me
Old 01-20-2011, 09:59 AM   #10
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Originally Posted by failelectric View Post
UF cable has limitation on installation through buildings.
Care to explain?
Old 01-20-2011, 11:23 AM   #11
Seriously? You know "great" electricians that don't own or know how to use a code book?
Old 01-20-2011, 11:26 AM   #12
Jesus Scott
electricmanscott's Avatar
Rewards Points: 232
You have two totally different issues you are asking as one question.
Romex is allowed in conduit, length is not an issue.
Romex is not allowed in wet locations. The inside of conduit in a wet location is considered a wet location.
Life is hard
The Following User Says Thank You to electricmanscott For This Useful Post:
Old 01-20-2011, 11:27 AM   #13
Jesus Scott
Rewards Points: 232
This must be your first day on the forum.
Life is hard
Old 01-20-2011, 11:29 AM   #14
Speedy you are obviously the man buddy. I am on the road right now and forgot my code book in my work truck. I was just looking for a little guidance. Thanks for your helpful reply. I wish I could have learned under you, then I might be the best electrician worthy of acting like an electrical god....
The Following User Says Thank You to eantonyg For This Useful Post:
Jbird66 (01-20-2011)
Old 01-20-2011, 02:31 PM   #15
Wow. You read way more into that than I intended.
You said you thought the code said a certain thing. You did not say you didn't have your book with you. Now today you say it is in the truck. Sorry that I assumed you did not have a code book.
What code cycle are you under? We can quote you the text if you need it. I have several editions in my phone if no one else chimes in.
Old 02-10-2011, 05:19 PM   #16
Romex has THHN insulation, not the dual rated insulation of THHN/THWN that you find on most reels of THHN. No W, no wet location.
Flycaster is offline   Reply With Quote
Old 02-10-2011, 05:24 PM   #17
Rewards Points: 272
Actually NM cable can have any 90C rated wire that the manufacturer wants to use. It may be dual rated or not but since it is not marked then it cannot be used outdoors even if it is in conduit.
Old 02-10-2011, 05:42 PM   #18
child please.....
NolaTigaBait's Avatar
Rewards Points: 14
I NEVER do that
REMOVED
Old 02-10-2011, 06:02 PM   #19
Romex has THHN insulation.........
Prove it.
Old 02-10-2011, 06:04 PM   #20
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Rarely have i gotten romex with printed Thhn/thwn on the conductors, I'd say 500' out of about one million feet i've installed.
romex/conduit 2leggedogwbrassballs General Electrical Discussion 85 11-27-2011 01:45 AM
Romex vs conduit hardworkingstiff General Electrical Discussion 89 01-12-2010 05:58 AM
Romex in flexible metal conduit waco General Electrical Discussion 6 01-07-2010 05:14 PM
Mc Or Romex Or Bx Nitro9119 General Electrical Discussion 3 05-19-2008 09:48 PM
Romex Where Not To Use BILL General Electrical Discussion 3 03-11-2007 10:53 AM