Originally Posted by alann53
No one answered this question. Is it permissable to run romex or any other cable through conduit?
334.15
(C) In Unfinished Basements and Crawl Spaces.
...NM cable installed on the wall of an unfin-
ished basement shall be permitted to be installed in a listed
conduit or tubing or shall be protected in accordance with
300.4. Conduit or tubing shall be provided with a suitable
insulating bushing or adapter at the point the cable enters
the raceway. The NM cable sheath shall extend through the
conduit or tubing and into the outlet or device box not less
than 6 mm (1⁄4 in.). The cable shall be secured within
300 mm (12 in.) of the point where the cable enters the
conduit or tubing. Metal conduit, tubing, and metal outlet
boxes shall be connected to an equipment grounding con-
ductor.