Originally Posted by Thayer
I couldn't find a reference in the NEC regarding this situation. There is both a gas line and a bonded telephone cable running between the two buildings. I was originally hired to install the telephone cable between the two , so I know that it is bonded at both ends via the metallic shield. I noticed the power situation later.
Grounding and Bonding, Article 250, section 250.32.
250.32 (B)(2)
Grounded Conductor. Where (1) an equipment
grounding conductor is not run with the supply to the build-
ing or structure, (2) there are no continuous metallic paths
bonded to the grounding system in each building or struc-
ture involved, and (3) ground-fault protection of equipment
has not been installed on the supply side of the feeder(s),
the grounded conductor run with the supply to the building
or structure shall be connected to the building or structure
disconnecting means and to the grounding electrode(s) and
shall be used for grounding or bonding of equipment, struc-
tures, or frames required to be grounded or bonded. The
size of the grounded conductor shall not be smaller than the
larger of either of the following:
(1) That required by 220.61
(2) That required by 250.122