Old 06-03-2012, 02:56 AM   #1
Default Size of cable compared to breaker
I want to confirm that:
for example: Breaker size is 80 AT
feeder size should carry out 80A
OR feeder size should carry out 90A
OR feeder size should carry out 70A
m sleem is offline   Reply With Quote
Old 06-03-2012, 08:12 AM   #2
Chief Electron Relocator
A feeder with an ampacity of 70a on an 80a breaker is a violation.
Old 06-03-2012, 08:17 AM   #3
mbednarik's Avatar
Cable size should be enough to carry the load applied. example, you have a 50 amp continuous load. 50 X 125% = 62.5 amp load. The conductors would have to be large enough to carry 62.5 amps after any/all derating for temp or bundling. Now reference standard OCPD (overcurrent protection device) sizing in 240 to find that would would put that general load on a 70 amp OCPD. If the type of load is any found in table 240.4 G special OCPD dizing applies, refer to the corresponding art.
mbednarik is online now   Reply With Quote
Old 06-03-2012, 08:20 AM   #4
but i know we can size the feeder by the previous step of the breaker....but i'm not sure this in regard to all type of loads or only motors.
Old 06-03-2012, 08:22 AM   #5
976-EVIL
mcclary's electrical's Avatar
Way too broad of a statement.
What if it's an outside tap? What if it's a tap? What if these are transformer secondary conductors with no overcurrent protection?
Old 06-03-2012, 08:24 AM   #6
976-EVIL
If your feeders ampacity is not corresponding to a common size breaker, you can got to the next size up as long as you're not over 800 amps.
There is a standard size 70 amp breaker, so you can't just go to 80.
Old 06-03-2012, 08:25 AM   #7
Depends on who's code you are referring to.
I am only familiar with the NEC.
Old 06-03-2012, 08:26 AM   #8
Originally Posted by mcclary's electrical View Post
Way too broad of a statement.............
The OP is way to ambiguous for anything else.
The Following 4 Users Say Thank You to 480sparky For This Useful Post:
BBQ (06-03-2012), Celtic (06-03-2012), mcclary's electrical (06-03-2012), nolabama (06-04-2012)
Old 06-03-2012, 08:55 AM   #9
This statement confuses me(along with everybody else). You size your circuit breaker to be less than the maximum current carrying capacity of your cable.
Your ciruit breaker is there to protect the cable and nothing else.
If you put an 80amp CB on a cable that is rated to a maximum of 70amps that is violation of any code in any country through out the world period....(sorry drunk)
Aussielec is offline   Reply With Quote
Old 06-03-2012, 10:08 AM   #10
could you show an example for this case ?.......our friends deny it.
Old 06-03-2012, 10:12 AM   #11
animal lover /rat bastard
wildleg's Avatar
as I posted in your other thread on almost the same subject, the NEC does not apply to your situation if you are in a Saudi Territory
i'm egyptian but i'm working in saudi arabia. ....
Originally Posted by wildleg View Post
ok, I confirmed that the NEC does not apply, so all the other replies to your motor feeder thread simply do not apply, unless you are not in a Saudi Arabian territory. This is from article 401 of the Saudi Building Code (Electrical)
12-3
Selection of electrical equipment
12-3.1
General
Every item of electrical equipment used in electrical installations shall
comply with the relevant Saudi standards as are appropriate. In the absence
of Saudi standards, the equipment shall comply with the appropriate
international standards (IEC, ISO, or ITU). Where there are no applicable
standards the item of equipment concerned shall be selected by special
agreement
Old 06-03-2012, 10:13 AM   #12
Chris Kennedy's Avatar
From the 2008 NEC
240.4(B) Devices Rated 800 Amperes or Less.
The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
Bulldozers and Dirt
The Following User Says Thank You to Chris Kennedy For This Useful Post:
m sleem (06-04-2012)
Old 06-03-2012, 10:18 AM   #13
Originally Posted by Chris Kennedy View Post
From the 2008 NEC
so clear .....very nice
Old 06-03-2012, 10:18 AM   #14
From the 2008 NEC
Old 06-03-2012, 10:28 AM   #15
Interesting, not something you hear often about the NEC.
Bulldozers and Dirt
The Following 2 Users Say Thank You to Chris Kennedy For This Useful Post:
erics37 (06-03-2012), m sleem (06-04-2012)
Old 06-03-2012, 01:48 PM   #16
erics37's Avatar
As you can tell from extensively researching the Saudi electrical code, it is rather lacking, which is probably why the OP is here asking this stuff. Why do you care what guideline they are under?
The Following User Says Thank You to erics37 For This Useful Post:
Old 06-03-2012, 02:23 PM   #17
B4T
ET Road Warrior
B4T's Avatar
This goes along with post #12..
240.6 Standard Ampere Ratings.
(A) Fuses and Fixed-Trip Circuit Breakers. The standard
ampere ratings for fuses and inverse time circuit
breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50,
60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300,
350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000,
2500, 3000, 4000, 5000, and 6000 amperes. Additional
standard ampere ratings for fuses shall be 1, 3, 6, 10, and
601.The use of fuses and inverse time circuit breakers with
nonstandard ampere ratings shall be permitted.
Old 06-04-2012, 07:02 AM   #18
wildleg's Avatar
Don't you think that it is appropriate to apply the code that specifically applies to the situation ? the Saudi code was initiated in 2007, and the section I quoted specifically references three other codes to use if the letter of their Article 401 isn't clear. The IEC is one of the codes that applies, but nowhere is the NEC referenced. Would you be so quick to quote European codes for work in the US ? I doubt it. I can't for the life of me understand why you would be so quick to defend the quoting of a code that doesn't even apply to the installation, given the information that was stated ? If there is no reference in their code to the NEC, doesn't it make you consider the notion that there is a reason for that ?
Old 06-10-2012, 12:04 AM   #19
ok but what about 20% spare capacity for the feeder and the breaker size.
50A continuous load x 125% = 62.5 amps
20% spare capacity = 75 amps
use 80 amp breaker and size feeder to carry not less than 80 amps= 4 awg
[not counting deration for temp or bundling]
1capybara is offline   Reply With Quote
Old 06-10-2012, 12:44 AM   #20
erics37's Avatar
Nothing in the code requires that you size for spare capacity. If you have a calculated continuous load of 62.5 amps and you could find a 62.5 amp overcurrent device then you could use that. Otherwise you can adjust the OCPD size to one of the sizes on the standard list in 240.6. Some feeders (like ones supplying motors for instance) don't allow you to size to the next standard OCPD up, so in those cases you're stuck using the next size down.
breaker size All Current NEC Code Forum 6 05-18-2012 12:02 PM
SER cable egc size electricmanscott NEC Code Forum 6 11-21-2011 08:44 PM
wire size and breaker size D neitzke General Electrical Discussion 3 07-14-2011 03:00 PM
Compressor breaker size bruddamon General Electrical Discussion 3 07-06-2011 03:45 AM