Transformer install - Electrician Talk - Professional Electrical Contractors Forum
Old 09-08-2016, 02:13 AM   #1
Arrow3030's Avatar
Rewards Points: 122
Default Transformer install
I'm looking for validation. I'll list disputed areas related to my particular project numerically.
1) A Delta/Wye transformer requires an OCPD on the secondary.
2) The secondary OCPD is allowed to be 125% the value of the transformer name plate. Next standard size allowed.
3) The secondary conductors must have an allowable ampacity greater than or equal to the secondary OCPD.
4) The allowable ampacity of the primary conductors must be greater than or equal to the rating of the transformer.
5) The primary OCPD is allowed to be 250% the value of the transformer name plate. Next standard size allowed.
*No continuos loads
6) Why did the dude before me try to tripple tap an outdoor transformer, bring the secondary cond's in the building with no OCPD, continue the run indoor for 50,75 & 100' respectively and terminate in three main lug load centers?
Arrow3030 is offline   Reply With Quote
Old 09-08-2016, 05:26 AM   #2
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,884
Certainly you have a problem.
Is this a farm?
Old 09-08-2016, 08:45 AM   #3
Arrow3030's Avatar
Rewards Points: 122
Not a farm
Old 09-08-2016, 09:43 AM   #4
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 588
*No continuos loads
there are a lot of rules, as well as exceptions to the rules, in 450. You need to provide a little more information: are these services ? is the transformer owned by the poco ? are the conduits into the building underground or encased ? are the panels main breaker ? 450 has all the answers except the ones relating to the service, by the numbers, but if you provide a little more info your questions are easy to answer.
Old 09-08-2016, 10:00 AM   #5
Rewards Points: 1,224
*No continuos loads
Item 4 is not correct. The ampacity of the primary conductors must be equal to or greater than the OCPD that supplies them.
There are no provisions in either Article 240 or 450 that permit the primary conductors to be connected to an OCPD that has a rating greater than the ampacity of the conductors.
Arrow3030 (09-08-2016)
Old 09-08-2016, 10:09 AM   #6
Arrow3030's Avatar
Rewards Points: 122
Not a service.
Customer owned transformer.
Conduits are underground to the building then continue in emt inside the building.
No discos on the secondary (feeds into main lug panels, not main breaker)
Old 09-08-2016, 10:13 AM   #7
Rewards Points: 15,800
An out door transformer makes one think in terms of underground secondaries terminating at OCPD within each panel.
Is such the case, here ?
Old 09-08-2016, 10:21 AM   #8
Arrow3030's Avatar
Rewards Points: 122
Nope. Previous electrician was planning to feed main lug panels with no secondary OCPD. The line diagram would go primary OCPD to transformer to three main lug load centers.
Old 09-08-2016, 12:46 PM   #9
Semper Fidelis
Not a farm
Ok then. You have to correct it.
The Following User Says Thank You to Suncoast Power For This Useful Post:
Old 09-08-2016, 02:16 PM   #10
Arrow3030's Avatar
Rewards Points: 122
Right on, thanks. My plan for the secondary is to come into a main breaker panel at the point of entry. Then use feeders out of that to the main lug subs. This is my first real world transformer so I appreciate everyone's help.
I'll size the primary OCPD to 125% the trans and use a conductor with greater or equal allowable ampacity.
I'll size my secondary to 125% the transformer and use conductors with equal or greater ampacity.
What I don't understand is why I'd want to size the primary to 250%. That seems wasteful since the conductors have to be sized to the OCPD. Anyone have insight on why using a higher percentage on the primary vs the secondary is beneficial?
Old 09-08-2016, 03:15 PM   #11
Rewards Points: 1,686
The most common curpit is inrush current that one of few reason why the OCPD is set for max of 250% .,,
It work both ways in upstep or downstep fashion., but keep in your mind the upstep verison is harder so expect more inrush current when first engerized it.,
Transformer neutral bond sizing (paralleled secondary) haltonelectrician Canadian Electrical Code Forum 27 06-19-2016 06:21 PM
3 phase transformer single phase supply Ultrafault General Electrical Discussion 24 06-12-2016 11:47 AM
has anyone ever install a 120/208 to 347/600 transformer? mike883 General Electrical Discussion 7 05-14-2016 10:08 AM
Transformer Bonding CES Services and Service Equipment 25 04-22-2016 11:54 PM
Can SDGE require my customer to pay for transformer Jeremy9 General Electrical Discussion 7 04-07-2016 06:01 PM