Old 11-18-2009, 02:40 PM   #1
Default TVSS Panel Tie-In
I have a situation which requires installing a external TVSS on a branch panel that is full. I can either install a CB somewhere near the top of the box and sneak-in under the bus lugs (against code) or what? Any bright ideas?
Control4_Ever is offline   Reply With Quote
Old 11-18-2009, 03:18 PM   #2
Jobless Extraordinaire
Grimlock's Avatar
Is there room to add a small sub? Move a couple circuits to it?
Grimlock is offline   Reply With Quote
Old 11-18-2009, 03:45 PM   #3
They just went down with drywall but yes, I could do this. The concern I have is that I need to protect loads located on the main panel. The distance from the TVSS to the sub and then to the target loads is much to far for the TVSS to be effective.
Old 11-18-2009, 04:13 PM   #4
Grimlock's Avatar
What type of panel and TVSS are you working with? Is this Resi or Comm?
Old 11-18-2009, 04:22 PM   #5
EE1
They are some manufactuers that offer surge circuit breakers that provide whole panel protection while not using up any spaces in the panel. See this link. http://www.stopsurges.com/SIEMENS-QS...20-QSA2020.htm
EE1 is offline   Reply With Quote
Old 11-18-2009, 06:29 PM   #6
Stiff Member
idontknow's Avatar
two words, tandem breakers.
idontknow is offline   Reply With Quote
Old 11-18-2009, 06:40 PM   #7
JayH's Avatar
Two summers ago we added these same type to protect over 25 panels during a school remodel (3P 4W 208V.) Very cost efficient and effective.
Upping my post count one mistake at a time!
JayH is offline   Reply With Quote
Old 11-18-2009, 08:48 PM   #8
You should read thru article 285 NEC, installation after the main disco. is
allowed just about anywhere, it's only two pages !!
Frank, Arizona,USA
It's what you learn after you know it all that counts
Benaround is offline   Reply With Quote
Old 11-18-2009, 08:52 PM   #9
Whats the NEC?
Sparky480 is offline   Reply With Quote
Old 11-18-2009, 08:59 PM   #10
Originally Posted by Sparky480 View Post
Whats the NEC?
In your case it would be" Never Ending Comments"
Frank, Arizona,USA
Old 11-18-2009, 09:40 PM   #11
Old 11-19-2009, 12:00 PM   #12
TVSS requires 2 poles so a quad-tandem breaker would displace one additional slot. I would need to gang on two wall outlet circuits to make that happen. Q23020 breaker would be the closest thing to working though. TVSS is Leviton 54000.
Old 11-19-2009, 09:50 PM   #13
Stiff Member
idontknow's Avatar
No silly, take 4 single pole breakers of the same amperage in your panel. Replace those 4 breakers with 2 tandem breakers. You'll now have 2 open spaces to install your new double pole breaker to power your TVSS
Old 11-20-2009, 12:18 AM   #14
sparks134's Avatar
yep yep!
sparks134 is offline   Reply With Quote
Old 11-21-2009, 09:47 AM   #15
JohnJ0906's Avatar
You first need to make sure that your panel is rated for tandem breakers - not all of them are.
John from Baltimore
"One day at a Time"
panel drm Code Violation Discussion 16 03-04-2010 07:25 AM
200 amp panel bobelectric General Electrical Discussion 18 08-04-2008 08:48 PM
Tvss ohmontherange General Electrical Discussion 4 07-06-2008 12:01 PM
TVSS Hows it work? Chris Kennedy Services and Service Equipment 1 02-29-2008 10:03 PM
400 Amp Panel ramsfield NEC Code Forum 4 02-20-2008 05:59 PM