Using metal junction box screw for grounding? - Electrician Talk - Professional Electrical Contractors Forum
Old 09-11-2007, 05:34 PM   #1
Default Using metal junction box screw for grounding?
I have read several articles that say its acceptable to use the screw that comes with the metal box for grounding. The two silver ones usually used to attach a fixture. As long as that screw is only used for that purpose and none other.
Now the NEC says you must use a green hexagonal screw as the grounding screw for the metal box. It never talks about using other screws already attached.
Safety wise, everything is grounded. But would this pass inspection? Thoughts?
shocking is offline   Reply With Quote
Old 09-11-2007, 06:22 PM   #2
JohnJ0906's Avatar
If you use the screw that comes with it, how will you secure the cover, plaster ring, fixture, etc? If you use it to connect the EGC, you can't use it for anything else.
I just use a green, hex head 10/32. You know, a ground screw. Why give an inspector something to fuss over?
John from Baltimore
"One day at a Time"
Old 09-11-2007, 06:30 PM   #3
Lets say your putting up a ceiling flourescent light where you use toggle bolts.
Then you can use the junction screw as a grounding screw because its not used for the fixture support.
Rare occasions would this be used anyway.
Old 09-11-2007, 07:04 PM   #4
Speedy Petey's Avatar
Rewards Points: 1,620
Wanna tell us where you got this erroneous information from.....
Old 09-11-2007, 07:10 PM   #5
Rewards Points: 3,855
I was waiting for someone to ask that.
It has to be green and hexagonal on receptacles, but the NEC doesn't happen to say that about box bonding screws.
Old 09-11-2007, 07:23 PM   #6
JohnJ0906's Avatar
I figured I'd throw out the NEC reference.
250.148(C) Metal Boxes.
A connection shall be made between the one or more EGCs and a metal box by means of a grounding screw that shall be used for no other purpose or a listed grounding device.
John from Baltimore
"One day at a Time"
Old 09-11-2007, 08:10 PM   #7
My mistake Speedy...it says the screw that you use must be that. E.g. Dont use a self tapping metal screw for grounding.
So it looks like the screw that comes already with the metal boxes may be used for grounding, as long as they are used for no other purpose.
Old 09-11-2007, 10:24 PM   #8
jbfan's Avatar
Rewards Points: 88
That may happen 1 out of 50 times you use a metal J-box?
get some 10/32 screws and use the threaded hole and use the cover screws for that, covers.
"The problem isn't that Hillary Clinton lies. We all know she lies. The problem is that her supporters don't seem to care"
jbfan is offline   Reply With Quote
Old 09-11-2007, 10:59 PM   #9
Y'think that much?
In almost 20 years I don't think I've done this once.
I agree. EVERY metal device or fixture box has a threaded 10/32 hole. Use it.
Old 09-12-2007, 08:30 AM   #10
jbfan's Avatar
Rewards Points: 88
Y'think that much?
I had to come up with some kind of number.
1 in a million did not sound encouraging
Old 09-14-2007, 12:38 AM   #11
Live Wire
Reddy Kilowatt's Avatar
Lightbulb
I've been known to do this from time to time, is this prohibited by the NEC?
Thanks
Reddy Kilowatt is offline   Reply With Quote
Old 09-14-2007, 12:42 AM   #12
Thanks
Yeah, there's a prohibition against sheet metal screws for grounding. Oddly, there's no prohibition against worse stuff like wood screws, drywall screws, railroad spilkes, nails, etc.
Old 09-14-2007, 02:29 PM   #13
Ax grinder
raider1's Avatar
Rewards Points: 1,080
250.8 has been changed to eliminate this problem in the 2008 NEC.
Here is the new wording in that section:
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods.
Grounding conductors and bonding
jumpers shall be connected by one of the following
means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding
equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than
two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
(B) Methods Not Permitted.
Connection devices or fittings
that depend solely on solder shall not be used.
Chris
Old 09-14-2007, 02:37 PM   #14
Wow...
So I guess Im wrong again... we are allowed to use self tapping screws from now on...
We can use anything we want now for that matter....
what if you use electrical tape to secure the ground to boxes... lol... j/k
Old 09-14-2007, 02:43 PM   #15
NO. A "Thread-forming machine screw" is NOT a self tapping screw.
Old 09-14-2007, 04:17 PM   #16
Ax grinder
raider1's Avatar
The typical self tapping screw will not meet the 2 threads fully engaged part of that requirment.
Here is a pitcure of a thread forming screw.
Chris
Old 09-14-2007, 05:32 PM   #17
That's good news.
A self drilling machine screw will work now too.
Old 09-21-2007, 10:15 AM   #18
Pierre Belarge's Avatar
Rewards Points: 150
What is a
"6) Thread-forming machine screws that engage not less
than two threads in the enclosure"
"thread-forming machine screw"...I am not sure that I have ever heard that term before.
Pierre Belarge is offline   Reply With Quote
Old 09-21-2007, 11:38 AM   #19
Ax grinder
raider1's Avatar
Originally Posted by Pierre Belarge View Post
What is a
Pierre,
The picture that I posted is of a thread-forming ground screw. The threads of the screw are designed to cut and form threads in the metal that they are being screwed into.
Chris
Old 10-03-2007, 08:51 PM   #20
Rewards Points: 25
I have sadly seen the EGC pinched between the cover and the box before.
romexrocket is offline   Reply With Quote
Junction Boxes Geraldo General Electrical Discussion 13 09-13-2014 08:00 AM
Adding ground screw n0c7 NEC Code Forum 33 10-21-2008 08:58 PM
Question about removing a screw type fuse box... OmegaBunny General Electrical Discussion 3 09-15-2008 07:48 PM
blown up screw driver dadadan Tools, Equipment and New Products 19 04-24-2008 07:34 AM
Grounding metal boxes Mackie NEC Code Forum 16 03-22-2008 12:36 AM