Is there a code for labeling wires?
jtashaffer is offline   Reply With Quote
Old 12-15-2010, 04:08 PM   #2
Speedy Petey's Avatar
Rewards Points: 2,266
In what context? Can you give us some more detail?
Old 12-15-2010, 07:25 PM   #3
Dierte's Avatar
Rewards Points: 250
I believe that the only code is based on colors.
Dierte is offline   Reply With Quote
Old 12-15-2010, 09:19 PM   #4
Coffee drinking member
Wirenuting's Avatar
Rewards Points: 2,540
If your referring to control wiring, then yes there is a standard.
You number your wires & termination points based on your wire line diagram. It all "flows" thru the equipment.
But that is past the point of NEC wiring requirements.
Old 12-26-2010, 08:21 PM   #5
Rewards Points: 150
310.12 Conductor Identification '08 code
jusme123 is offline   Reply With Quote
Old 12-26-2010, 08:30 PM   #6
NC Sparky
wirenut71's Avatar
Send a message via Yahoo to wirenut71
Give some more info.
wirenut71 is offline   Reply With Quote
Old 12-26-2010, 09:19 PM   #7
Rewards Points: 150
The NFPA 79 has some information on labeling conductors.
Wingnut is offline   Reply With Quote
Old 12-26-2010, 11:38 PM   #8
310.12 Conductor Identification.
(A) Grounded Conductors. Insulated or covered grounded
conductors shall be identified in accordance with 200.6.
(B) Equipment Grounding Conductors. Equipment
grounding conductors shall be in accordance with 250.119.
(C) Ungrounded Conductors. Conductors that are in-
tended for use as ungrounded conductors, whether used as a
single conductor or in multiconductor cables, shall be fin-
ished to be clearly distinguishable from grounded and
grounding conductors. Distinguishing markings shall not
conflict in any manner with the surface markings required
by 310.11(B)(1). Branch-circuit ungrounded conductors
shall be identified in accordance with 210.5(C). Feeders
shall be identified in accordance with 215.12.
Exception: Conductor identification shall be permitted in
Can't just put in the code article, have to actually say something besides.
Old 01-19-2011, 10:31 AM   #9
Default Label Printers?
Anyone using a label printer to mark their cables? If so, which features are essential, and which features would you like to see that don't already exist?
Andrew44 is offline   Reply With Quote
Old 01-19-2011, 11:18 AM   #10
Rewards Points: 502
Not code, but your best bet is to "reverse address" all your wiring if your in any kind of plant/generation station, etc.
Don't let fear be your guide!
Rockyd is offline   Reply With Quote
Old 01-19-2011, 12:41 PM   #11
Electron Flow Consultant
sparky970's Avatar
Rewards Points: 952
I like to tag where it's at and where it's going.
Old 01-19-2011, 01:56 PM   #12
Rewards Points: 1,516
im using a pretty basic brady thermal printer (about 150$), you can choose between many types of self-adhesive tags (i prefer nylon tags). i dont like heatshrink type tags since you have to disconnect wire for identification.
4 wire CAT 5.. B4T Structured Wiring 8 05-19-2010 01:48 AM
Wire Labeling System LogicDB PLCs, VFDs, Motors and Controls 12 04-16-2010 07:17 PM
Security camera cable & wire next to 14g wire for outdoor lights agent99 Structured Wiring 5 09-17-2009 04:36 PM
Labeling a panel caseyelectric General Electrical Discussion 53 07-20-2009 01:08 PM
Labeling Romex in panels. MDShunk General Electrical Discussion 41 02-03-2009 03:27 PM