Originally Posted by a-bulb
What is this? Run 2- 2 wires instead?
Naw, the ones I've run across, they use one 14-2 romex for the traveller. They then feed it on one end and switch on the other end. Here's the real kicker: you still have to have a feed in both ends so the switch leg can get its neutral. With 14-3, you acclomplish this with the white wire bringing the neutral over. What's really screwed up is that to do a two wire traveller "properly", you would need to run the same feed to both ends of the three way, but that's not how it usually happens. They normally steal the neutral they need from another circuit, which is usually closer than running the same feed around. Well, it works, until you service the three way. You kill the breaker that the three way is fed with, but what happens when the neutral gets a load on it from that other circuit that you got it from? Nice pleasent surprise.