Old 03-22-2007, 10:54 PM   #1
Default MC cable and duplex connectors
I know that you supposedly don't have to use red heads with MC connectors, because they're supposed to be self-bushed. Do you need to use red heads when you're using a duplex MC connector? They don't seem like they have any way to bush each MC, and you might legitimately need to use a red head. I know some people are going to say -always use a red head- but I'm trying to figure out the real answer and not what a person might do.
Thanks.
Rikki is offline   Reply With Quote
Old 03-22-2007, 11:19 PM   #2
Always use a red head! (sorry, couldn't resist)
I don't know, but I see where you're coming from. Sounds like a question for NEMA, since that bulletin about not requiring anti-short bushings originally came from them. I have no idea how you ask NEMA a question, though.
Old 03-23-2007, 05:31 AM   #3
Joe Momma's Avatar
I've always known "red-heads" as a concrete anchor, but for MC I assume you mean "a$$holes", or as some fruity guy called them, "rose-buds".
I've only used anti-shorts with the type of MC connector that has a set-screw. The push in type; double or single barrel, I don't use them and have yet to see a problem.
Though I will point out that a quality installation depends on the installer.
Joe Momma was here
Old 03-23-2007, 11:16 AM   #4
Ax grinder
raider1's Avatar
The reason that you don't need to use anti-short bushings on MC cable is that the listed connectors for use with MC cable come with bushings in the connector themselves.
I still always use the anti-short bushings on my MC cable. (a little extra protection goes a long ways. )
Chris
Old 07-08-2009, 05:15 PM   #5
Default No anti-short needed?
So am I correct in understanding that the NEC does not require anti-shorts for MC? I know ART 320.40 is very specific about requiring them for AC cable, but isn't all MC cable inherently AC. What's difference between AC, MC and BX? Someone, please?
ssandoval is offline   Reply With Quote
Old 07-08-2009, 05:49 PM   #6
Ax grinder
raider1's Avatar
No, the sheath of standard MC cable is not listed as EGC and the cable contains an insulated EGC.
AC cable has a small aluminum bond wire run in direct contact with the interior of the cable sheath that will help the sheath provide a low impedance fault current path without an additional insulated EGC.
Also "BX" is a trade term for AC cable similar to the term "Romex" for NM cable.
Chris
Old 07-08-2009, 06:01 PM   #7
electricalperson's Avatar
a lot of guys use romex connectors for MC. i hate doing that makes me feel like peter d
Old 07-08-2009, 06:07 PM   #8
Black4Truck's Avatar
Peter D uses connectors??
Black4Truck is offline   Reply With Quote
Old 07-08-2009, 06:20 PM   #9
Ax grinder
raider1's Avatar
If the romex connector is not listed for MC cable that could be a big problem. The sheath of the MC cable must still be bonded and you need to use a connector that is listed for MC cable.
Chris
Old 07-08-2009, 06:23 PM   #10
Chris
only difference i see between an arlington MC connector and an arlington 3/8 romex connector is the bottom that sits inside the panel. the MC connector keeps all the wire in the center and a romex connector doesnt. i never looked up the UL listing of that stuff. i use MC connectors anyway
Old 07-08-2009, 07:37 PM   #11
Professional Nit Picker
AC generally has the conductors wrapped in paper and MC generally has the conductors wrapped in plastic.
Old 07-08-2009, 09:34 PM   #12
I think this is nit-picking.. put the thing on.. the time it takes to accomplish this is seconds.
Even a HO could do this and the red heads are free
Old 07-08-2009, 10:34 PM   #13
jsb
is anyone out there using mcap?
jsb is offline   Reply With Quote
Old 07-09-2009, 11:59 AM   #14
Lurker...
LJSMITH1's Avatar
Perhaps this will help explain where anti-shorts are to be used and why. MC is not the same as AC - even though it looks similar.
As for Southwire's MCap, what exactly are you looking for as far as info?
LJSMITH1 is offline   Reply With Quote
Old 07-09-2009, 12:01 PM   #15
Lurker...
LJSMITH1's Avatar
Chris
Its a bit more than just a bonding requirement. There is also a cable stop requirement for AC/MC fittings. There is no similar requirement for NM.
Bottom line is always use fittings listed for the particular type and size cable/conduit you are using. The label on the box should tell you just about everything.
Old 07-09-2009, 12:02 PM   #16
jsb
I have all the info I need I was just curious what parts of the country were using it
Old 07-09-2009, 12:05 PM   #17
Lurker...
LJSMITH1's Avatar
Typically any area where MC/AC cable is widely accepted (i.e. NOT Chicagoland). It certainly does reduce the time to wire a job.
Be sure to use fittings listed for use with that cable.
Old 07-12-2009, 01:28 PM   #18
zappy's Avatar
And I always thought a a%#hole was a plastic bushing.
"In thee abundance of water, the fool is thirsty"
zappy is offline   Reply With Quote
Old 07-19-2009, 01:15 PM   #19
Default Anti-Short
The union guy has never had a problem, Because they don't call you to repair your problems,
Termination is offline   Reply With Quote
Old 07-19-2009, 03:43 PM   #20
JohnJ0906's Avatar
No, that's usually my helper.
John from Baltimore