Originally Posted by tmerc65
Using NFPA 79 as a guide I get
9.2.5.2.4 – If more than 1 start device is present then all start control devices shall be actuated concurrently.
9.2.7.5 – If there is more then 1 control station then only one station can be active at a time.
The reasons:
The operator would like multiple start and stop buttons on a machine that needs to be threaded in the beginning of the process. As he walked along threading the machine he would always have a place within reach to stop and start the machine as needed.
My way around the above standard would be to place the machine in a THREAD MODE that would only allow the machine to run at a slow speed (less then 250mm/sec) and the buttons that would not be labeled start but THREAD SPEED would only be active in this mode and do nothing when the machine is in RUN mode. Of course the STOP buttons would still work.
Am I on the right track.
I am not familiar with your code but I would not think that what you propose would be appropriate. I believe that what you want to do is ensure that person threading the machine has sole control.
If he is at Station 1, he could pass control to Station 2 and move to that position. From there he could pass control to Station 3 and so on. He may want to have the option to pass control back to Station 1 without completing the sequence but that would depend on the the safety of the particular application.
Another way to approach it may be to switch to threading mode and no stations become active until some kind of switch indicates that someone is at a station and locks out the other stations.
If 2 handed operation is required then there are options such as foot, hip, elbow switches and cables to act as stops and safeties.
You will have to decide the best way to give the operator sole control.