Go Back   Electrician Talk - Professional Electrical Contractors Forum > Electrical Trade Topics > Linework
Old 11-04-2009, 09:48 PM   #1
Burger Flipper
TOOL_5150's Avatar
Send a message via ICQ to TOOL_5150 Send a message via AIM to TOOL_5150 Send a message via MSN to TOOL_5150 Send a message via Yahoo to TOOL_5150
Default Substation video - I got a question.
This is a 10 second video of what looks like wires being blown up, and it looks like it was planed. Can anyone tell me what is going on here?
http://www.youtube.com/watch?v=DCyMS...eature=related
~Matt
Old 11-04-2009, 10:25 PM   #2
IBEW Local 970 Member
sparky970's Avatar
I'd say someone did't remove the safety grounds, before they closed the breaker.
Old 11-04-2009, 10:27 PM   #3
Burger Flipper
TOOL_5150's Avatar
AHH Whoops!!
~Matt
Old 11-05-2009, 12:07 AM   #4
Zog
Zog's Avatar
Those are protective grounds but that was a test, conducted by AB Chance if I recall.
Old 11-05-2009, 01:14 PM   #5
Energizing an indoor metal-clad medium-voltage switchgear with the ground set still connected is MUCH more ugly!
Rob
Old 11-05-2009, 05:10 PM   #6
Robotic Rat
nolabama's Avatar
Did the product pass or fail the test?
the more i learn the less i know
Old 11-05-2009, 05:15 PM   #7
EDM
EDM's Avatar
I was wondering that too. Is there supposed to be a dangerous blast like that?
I'm going back to work on Friday, no more time for foruming. Bye everyone!
EDM is offline   Reply With Quote
Old 11-05-2009, 05:32 PM   #8
Robotic Rat
nolabama's Avatar
If it is a ground strap that is designed to protect personnel I believe it should be able to handle the energy without energizing the line. I don't know that, however.
Old 11-05-2009, 09:19 PM   #9
A ground set might kinda, sorta, almost protect a person from the line being energized, but it's main purpose is to ground out induced voltages. If the protection relays were set fast and low, you'd likely be OK.
I never trust a ground set to protect me from a line being energized. I always disable the line some other way. A lot of guys don't though....
In an overhead line that's not grounded, voltage can be induced by capacitive coupling from other lines, static from wind, and a lot of other sources. If the line has been isolated for a while, and the ground set is attached, I've seen arcs an inch or two long. A nice little SNAP!!
Hint; make sure you attach the ground side first!
Rob
Old 11-06-2009, 09:59 AM   #10
Zog
Zog's Avatar
Protective grounds need to be rated for the available fault current in the system they are being installed on, they serve 3 functions.
1. To dissapate any induced or stored energy on the line
2. To create a 3 phase fault and trip the upstream protective device in case the line accidently becomes energized
3. To create a zone of equilized potential during the period of time the line is energized.
Proper installation is vital for creating an equipotential zone. For example, indoor 15kV switchgear, the ground is attached to the ground bar in the switchgear which is bonded to the substation ground, including the rebar in the concrete floor you are standing on. If the system becomes energized the line, the metal enclosure, and the rebar under your feet are all energized to the same potential (Until the OCPD activates) eliminating any voltage drop across the workers body.
Substation Batteries Andy Robson UK Electrical Forum 4 03-13-2009 02:47 PM
What insulation would be found in a 400kv outdoor substation craig2k8 General Electrical Discussion 5 06-21-2008 01:23 PM
protection of short line between power plant and substation m.s.j General Electrical Discussion 0 07-11-2007 01:08 PM
DIY video JohnJ0906 General Electrical Discussion 10 06-27-2007 07:17 AM
Medium voltage substation airdenver General Electrical Discussion 1 05-18-2007 09:19 PM