What is the output difference on a low voltage magnetic dimmer, as opposed to an electronic low voltage dimmer?
SparkYZ is offline   Reply With Quote
Old 12-16-2010, 09:39 PM   #2
BBQ
Salty Member
BBQ's Avatar
As I understand it the cheaper dimmer, produces an output like this
Which is OK for an incandescent lamp but not a magnetic transformer. The constant instant 0 volt to full volt spike cause inrush current each time overheating the transformer.
The better dimmer produces a wave more like this
A slow rise and sharp fall.
Old 12-16-2010, 09:43 PM   #3
SparkYZ's Avatar
Rewards Points: 506
A dimmer essentially shuts off the power to a luminaire each time the sine wave changes direction right? A cheaper (magnetic) one shuts it off before the peak, and a better one shuts if off after the peak...
So you could use a low voltage electronic dimmer on a magnetic fixture, couldnt you? It's kinda like a better, smoother, power supply (wrong wording, I know)
Old 12-17-2010, 04:16 AM   #4
This might answer your question:
http://www.lutron.com/ResourceLibrary/362219.pdf
Jackomo is offline   Reply With Quote
Old 12-17-2010, 07:20 AM   #5
Rewards Points: 410
It has to do with the transformer that you are dimming. If you have a low voltage light that has a magnetic trany then you would use a LV magnetic dimmer. If the trany is electronic then use an electronic LV dimmer. Now there are some LV electronic tranies that can be used with a standard dimmer but generally it will state that on the trany or somewhere. I have seen some WAC electronic tranies that did not need an electronic dimmer.
Old 12-17-2010, 09:25 AM   #6
Rewards Points: 250
The question I always had with this:
The transformer "may" said you can use it with a standard dimmer but I have never seen a standard Incandescent dimmer say you could use it with any electronic transformers. It comes down to a "listing" question.
Its kind of like GFI testers. Sure the GFI tester is listed to test GFI's but most GFI's are only listed to be "tested" by pushing the test button on the device..
And yes that is a fun question for the AHJ.
Jbird66 is offline   Reply With Quote
Old 12-17-2010, 09:33 AM   #7
Rewards Points: 410
Imo, the dimmer does not have to list every type of transformer or light that it can dimmer, but I may be wrong. If it states do not use with LV lighting that would be different. I have never had an issue with a Lutron ariadni dimmer on a lv fixture that stated it can be dimmed from a standard dimmer.
We can see this issue everywhere-- Siemens makes a breaker that will fit SQ. D and is listed for it but the panel states listed for sq. d breakers.... What do you do.
All standard incandescent recessed cans I have seen that I have seen are listed as incandescent luminaires. Now the CFL bulbs say they are listed for all cans????? Same issue.
Old 12-24-2010, 05:42 PM   #8
Light Emitting Decoration
Electric_Light's Avatar
Rewards Points: 1,820
If the dimmer and load are not matched for the application, you may experience malfunctioning or limited dimming range.
A two-wire fluorescent dimmer meant for Lutron TuWire and Philips-Advance Mark X actually works just fine with incandescent, but you'll have a disappointingly narrow dimming range.
Other way around, you'll experience flickering and limited dimming range. The flickering will lead to premature lamp failure.
The reverse-phase design which rises from zero, then cuts off at set point is designed specifically for electronic low voltage transformers that call for it. MLV transformers do not use reverse phase dimmer, though some have neutral for more stable operation.
Electric_Light is offline   Reply With Quote
Old 12-27-2010, 10:39 AM   #9
Rewards Points: 250
Stick with the Squre D breaker. Even though the Siemens breaker is listed, installling it in a Square D panel de-lists the panel by violating the limits on its UL listing.
Shorty Circuit is offline   Reply With Quote
Old 12-27-2010, 12:12 PM   #10
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
I actually have about a dozen GE40 amp DP breakers made for SQ D QO . bought them at a garage sale for $10.
Old 11-26-2013, 08:01 PM   #11
can a dimmer work with both electronic and magnetic transformers on the same switch leg?
I want to replace bad magnetic transformers for low voltage can lights with electronic transformers since they are cheaper and plentiful at the supply house. But would the dimmer work for a combination of both magnetic and electronic transformers?
paulgarett is offline   Reply With Quote
Old 11-26-2013, 08:51 PM   #12
Going_Commando's Avatar
Rewards Points: 292
Phuck the UL with a rusty spoon.
Old 12-11-2013, 04:11 AM   #13
ngsafety's Avatar
Magnetic dimmers use onward phase dimming, and electronic dimmers use overturn phase dimming
*link removed*
ngsafety is offline   Reply With Quote
Magnetic Trip only?? postalizer General Electrical Discussion 3 10-07-2010 09:56 PM
Magnetic Insulated Nutdrivers knowshorts Tools, Equipment and New Products 32 07-08-2010 04:46 PM
Magnetic starter problem copperhead General Electrical Discussion 10 03-10-2009 06:44 PM
Replacing 8, 2 lamp magnetic ballast lighting with electronic ballast and t8 lamps phish1985 General Electrical Discussion 4 03-02-2009 02:57 PM
Magnetic Dimmer JohnJ0906 General Electrical Discussion 12 09-17-2007 12:40 AM