04-24-2011, 12:46 PM
200 Amp, 3-phase, 120-208 Volt service
It's a restaurant. The existing panel only has I think it was 30 spaces. It is full of piggyback/tandem breakers and has a sub panel next to it (60 amp/8 space). There are a total of 51 spaces for the existing circuits. So I need to replace it and I guess my question is, is it ok for me to use 2 panels which would be the main lug feed through type. They would be 42 space panels. They would be identical panels. I would feed the second panel from the lugs of the first panel. Any problems with that?
04-24-2011, 12:50 PM
Fried Bologna um um good!
Nope. You could install as many panels as you want. I assume you are getting a feed thru panel with a main in it. The main would protect both panels that way.
The Following User Says Thank You to jwjrw For This Useful Post:
04-24-2011, 12:54 PM
Heavily Armed Member
I don't see why not as long as you have a main breaker it will be a big improvment.
04-24-2011, 12:55 PM
I thought I read somewhere that they are making 60 circuit load centers now.
04-24-2011, 12:57 PM
They are but they are big and not cheap where I am.
04-24-2011, 01:58 PM
Why do I have to have a main breaker? The existing install doesn't have one. It has a fused disconnect in a centrally located electric room which serves the entire shopping plaza.
04-24-2011, 02:00 PM
Ok so why must I have a main breaker in it? I'm treating it as a sub-panel since the disconnect is located elsewhere in an electric room. I'll keep the ground and neutral separated.
04-24-2011, 02:23 PM
I thought it was the service. If it has a disconnect no main needed.
04-24-2011, 02:58 PM
You should price with a main on it anyways. Might not be a huge difference? I like putting in mains as a design decision when the price is close. If it's a bid.. Money in your pocket.
04-24-2011, 04:13 PM
I've done this a lot.
The first panel needs to have either sub-feed lugs or feed-through lugs.
Sub-feed lugs are double lugs where it is fed, feed-through is a set of lugs at each end.
Which one you use will depend on how you want to feed the second panel.
Feed-through lugs usually have a longer can.
It's really common around here to have two panels daisy-chained together like this.
Rob
04-24-2011, 04:18 PM
Pretty typical arrangement where the load isn't that great, but the need for a lot of circuits is. Retail and office space are two instance where you often have a need for a ton of circuits but the overall load isn't that substantial.