600 amp parallel feed - Electrician Talk - Professional Electrical Contractors Forum
Old 06-12-2010, 09:47 PM   #1
Question 600 amp parallel feed
i have a 600 amp panel with parallel feeds in two different runs of conduit.
one run of conduit has 3 500 kcmil and a 4/0 for ground.
second one has 3 3/0 thhn and a 1 awg for ground.
(IS THIS CODE) can you run different size wire on a parallel feed.
industrialboy is offline   Reply With Quote
Old 06-12-2010, 09:50 PM   #2
Rewards Points: 5,198
Whether it is right or wrong is a consideration that you should have thought about before you pulled the wire...or you just trying to test us?
Old 06-12-2010, 10:01 PM   #3
Default 600 amp parallel feed
i'm a contractor who is setting up a new machine, and need to pull out of this panel
Old 06-12-2010, 10:22 PM   #4
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
The parallel conductors need to be the same length, material, size, insulaation, and terminated in the same manner. 310.4
Replies based on NEC 2014
Old 06-13-2010, 03:41 AM   #5
Rewards Points: 1,684
The answer is no you can not run diffrent size conductor it must be the same size as the other set of conductors and the length is the same and type as well.
Look up in 310.4 plus few other spots IIRC
And you will run some issue with unbalanced conductors current drawage { I am pas joking on this one }
Merci.
Marc
Old 06-13-2010, 09:45 AM   #6
Electric Al
oldtimer's Avatar
Rewards Points: 2,306
Merci.
Marc
Oui , Vous etes correct. Just practising my french.
Old 06-13-2010, 01:06 PM   #7
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,876
Feeder into the breaker or load side of the breaker.
Is this a feeder leaving the breaker and going to two separate loads or is this feeding the line side of the breaker?
Old 07-10-2010, 09:54 PM   #8
Rewards Points: 25
In agreement with the other posters, this is a code violation for parallel feeds. I want to add that this is a very dangerous situation. Remember that current will flow through the path of least resistance which, in this case, is the set of 500s. Most of the load will try to use this path, rendering the 3/0s useless. If the service is loaded to more than 430a, the 500s will overheat without tripping the breaker until there's a dead short inside the conduit. This condition can also result if there's any appreciable difference in the lengths of feeder conductors, even if they're the same size.
Mogie is offline   Reply With Quote
Old 07-10-2010, 10:07 PM   #9
Rewards Points: 250
Current is not guaranteed to divide in any specific quantity, resistance of conductors and resistance of connections together determine how much current flows on which conductor, you could easily have the 3/0 carrying the majority of the current if you have a higher resistance connection on the 500.
kwired is offline   Reply With Quote
Old 07-10-2010, 10:31 PM   #10
Rewards Points: 560
Totally wrong. The panel may work fine without much load but as others have said if the load gets up there you will have issues.
You need to have parallel 300kcm copper conductors if the calculated load on the panel is 570 amps or less. Art. 240.4(B) allows us to use the next size breaker -- 600 amps.
Your egc needs to be based on the 600 amp breaker from T. 250.122. This means you need a #1 copper conductor in both raceways.
When you say 4/0 for ground and #1 for ground are you meaning neutral or the EGC (equipment grounding conductor)?
Oil Spill Live Feed mattsilkwood Off Topic (Non Trade) 3 06-04-2010 05:56 AM
Feed thru panels... NolaTigaBait NEC Code Forum 11 05-18-2010 04:07 PM
Meterbase Feed Thru??? chenley NEC Code Forum 20 01-20-2010 07:01 PM
Garage Feed Mike Lamb Code Violation Discussion 2 12-04-2008 12:52 PM
feed a 400 rll77 Services and Service Equipment 19 04-02-2008 09:47 PM