Old 08-09-2009, 07:29 AM   #1
Default 9 unit plus house 800 amp 1 phase service
Ok recalculation 3 units @ 6912 va 3 units @ 11880 va 3 units @ 10,800 va # is total 4 the 3 units. Plus a house panel I am figureing 10,000 va 4 electric dryers 3,00 for washers @ 100 percent.
No A/C or Hot water but owner is not sure. I would like to have allowence for the future.
9- 100 amp panels for units 1 - 100 amp house
600 Amp single phase servie 120/240 or would u go 3 phase 120 / 208
Does this give me future room for ac per unit avg unit is 1,200 sq '
gemini13 is offline   Reply With Quote
Old 08-09-2009, 07:34 AM   #2
Chris Kennedy's Avatar
Originally Posted by gemini13 View Post
I was thinking that 2 300 per phase should be good for 800 amps .
Thats good for 570A. Whats the calculated load?
Bulldozers and Dirt
Old 08-09-2009, 07:39 AM   #3
wildleg's Avatar
400 Cu if you're using the 310.15 B 6 table (2005). but you might wanna do the load calc and see if you can go smaller.
Chuck Norris sleeps with a night light. Not because Chuck Norris is afraid of the dark, but the dark is afraid of Chuck Norris.
Old 08-09-2009, 08:02 AM   #4
You can apply this table to parallel conductors?
Bulldozers and Dirt
Old 08-09-2009, 08:21 AM   #5
Not Peter D
Bob Badger's Avatar
When you have a single service disconnecting means the conductors can not really be reduced in size other then what 240.4(B) allows.
IMO, no, not at all.
However Don G. has posted some CMP statements to the contrary. I would talk to the inspector before using T310.15(B)(6) to choose parallels from.
Bob Badger is online now   Reply With Quote
Old 08-09-2009, 08:44 AM   #6
wildleg's Avatar
hmmm, I wasn't sure, but I thought you could use it up to 800 (oops ? )
Old 08-09-2009, 09:20 AM   #7
I dont have know what sizw wire i need to parallel to disconnect. I dont have code book handy. I was thinking that 2 300 per phase should be good for 800 amps . I was thinking of running it in two 3' masts sisde by side into the disconnect.
You really going to a disconnect first, or to a CT can? Just wondering. I know that some PoCo's put a CT rack on the mast, near the weatherhead. I was mostly wondering where your CT's were going.
Old 08-09-2009, 09:22 AM   #8
310.15 (b) 6 is for single family dwellings. It does not apply here.
Old 08-09-2009, 09:34 AM   #9
Not Peter D
Bob Badger's Avatar
Why would there be any CTs?
Utility >>> 800 amp service disconnect >>> 10 meters >>> sub panels
Old 08-09-2009, 09:35 AM   #10
I was thinking 9 bedroom house with one big service. Duh. 9 units, plus a house. Okay, I see.
Old 08-09-2009, 09:35 AM   #11
Licensed Pro
Magnettica's Avatar
It applies to two-family and multi-family dwellings too, but not for any triple-phase dwelling services.
Vince Lombardi
Old 08-09-2009, 09:36 AM   #12
310.15(B)(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders.
For individual dwelling units of one-family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service-lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor.
Bulldozers and Dirt
Old 08-09-2009, 09:38 AM   #13
Not Peter D
Bob Badger's Avatar
Damn good point, he can not use that table for the service conductors. If the service remains single phase 120/240 he can use it for each units feeder (other than the landlord panel)
But in my area the power company will not supply an 800 amp single phase service.
Old 08-09-2009, 09:40 AM   #14
Not Peter D
Bob Badger's Avatar
No, not for the service conductors, only the feeders to each unit.
Old 08-09-2009, 09:42 AM   #15
Not Peter D
Bob Badger's Avatar
Chris,
For individual dwelling units of one-family, two-family, and multifamily dwellings .......
Old 08-09-2009, 09:42 AM   #16
Right. "For the individual dwelling units of... multifamily dwellings" That pretty much limits you to using that table for the conductors from the load side of each tenant meter to the tenant panel.
Old 08-09-2009, 09:48 AM   #17
Ah, I see, thanks guys.
Bulldozers and Dirt
Old 08-09-2009, 09:48 AM   #18
Licensed Pro
Magnettica's Avatar
So I understand this fully...
120/ 208 SEC's are sized to T310.16 but the feeders to each individual "sub panel" can be sized to 310.15 (B)(6).
Good?
Vince Lombardi
Old 08-09-2009, 09:52 AM   #19
Did anyone notice that the OP edited post 1?
Bulldozers and Dirt
Old 08-09-2009, 09:53 AM   #20
Not Peter D
Bob Badger's Avatar
Good?
If the service is 208Y/120 you can not use that table at all.
If the service is 120/240 it can be used for each feeder to each individual dwelling unit but the service conductors supplying all these feeders will have to be sized per 310.16
is this a 3 phase unit? vdubnluvn General Electrical Discussion 8 07-13-2008 09:53 AM
house service Rong General Electrical Discussion 60 05-31-2008 09:03 AM
three phase to single phase convertion. brick General Electrical Discussion 2 07-29-2007 07:55 PM
New house service... Dayne Services and Service Equipment 17 06-03-2007 09:36 PM
two phase or single phase jorge General Electrical Discussion 9 03-27-2007 01:06 PM