08-10-2009, 04:08 PM
|
#41
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by Magnettica
You could use 300 Kcmil THHN/ THWN copper conductors in parallel for 570 amps, or you could use 350 Kcmil in parallel for 620 amps. It depends on your calculated load. IMO if you're selling a 600 amp service then give them conductors that'll carry the full 600 amps.
If you choose to use the 300's, 1/0 copper for your water pipe electrode, and 2/0 if you choose the 350's.
|
yes I think ot will also depend on the lugs I believe I need them to be rated at 95
|
|
|
Join the #1 Electrician Forum Today - It's Totally Free!
ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!
Join ElectricianTalk.com - Click Here

|
Warning: The topics covered on this site include activities in which there exists the potential for serious injury
or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
08-10-2009, 05:13 PM
|
#42
|
|
Not Peter D
Join Date: Apr 2009
Location: South Eastern MA
Posts: 2,908
|
Quote:
Originally Posted by gemini13
well I have installed 2- 800 amp single phase service it's been awhile the last one was a 14 unit building.
|
Thats great.
Quote:
|
I was just askinkinh for some ideas
|
And I was just suggesting that before you waste to much time planing to check with the power company about what they are willing to supply that address with.
But if you feel like rolling the dice and perhaps redoing your work go for it.
|
|
|
08-10-2009, 05:36 PM
|
#43
|
|
Licensed Pro
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 2,784
|
Quote:
Originally Posted by gemini13
yes I think ot will also depend on the lugs I believe I need them to be rated at 95
|
Do you mean temperature rating of the lugs? If so, you'll need your equipment to be rated for 75º. Your THHN is rated for 75º as well. There is no such thing as a 95º temperature rating for equipment or conductors and very rarely is anything ever rated for even 90º.
You also want to take Bob's advice and contact the power company. Hopefully they'll provide you with an representative who's familiar with the wiring in the area of your job and can guide you through the process.
Also, how long will this service take you to build? 10 meters/ 10 disconnects/ and ten panels could take more than an hour or two. What will the people living in the building do while the power is shutoff?
If this is "one big side job" I suggest you pass this job off to your boss and let him handle it.
__________________
There's only one way to succeed in anything, and that is to give it everything.
Vince Lombardi
|
|
|
08-10-2009, 08:31 PM
|
#44
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by Bob Badger
Thats great.
And I was just suggesting that before you waste to much time planing to check with the power company about what they are willing to supply that address with.
But if you feel like rolling the dice and perhaps redoing your work go for it.
|
I have installed a service for a 14 unit building in that area years ago, but i do plan on talking with the power company once I have an idea what im going to do
|
|
|
08-10-2009, 08:37 PM
|
#45
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by Magnettica
Do you mean temperature rating of the lugs? If so, you'll need your equipment to be rated for 75º. Your THHN is rated for 75º as well. There is no such thing as a 95º temperature rating for equipment or conductors and very rarely is anything ever rated for even 90º.
You also want to take Bob's advice and contact the power company. Hopefully they'll provide you with an representative who's familiar with the wiring in the area of your job and can guide you through the process.
Also, how long will this service take you to build? 10 meters/ 10 disconnects/ and ten panels could take more than an hour or two. What will the people living in the building do while the power is shutoff?
If this is "one big side job" I suggest you pass this job off to your boss and let him handle it.
|
I am the boss the building is empty , and I was just getting ideas. Thanks for your concern, you may try not to be such a tool next time. I will install all the meters, and the house panel. Then we can restore power to the building that has been empty for 3 years.
|
|
|
08-10-2009, 08:38 PM
|
#46
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by gemini13
I am the boss the building is empty , and I was just getting ideas. Thanks for your concern, you may try not to be such a tool next time. I will install all the meters, and the house panel. Then we can restore power to the building that has been empty for 3 years.
|
diconnects and meters all one piece, they all bolt together. It is very easy to install I think you could do it.
|
|
|
08-10-2009, 11:18 PM
|
#47
|
|
Licensed Pro
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 2,784
|
Quote:
Originally Posted by gemini13
I am the boss the building is empty , and I was just getting ideas. Thanks for your concern, you may try not to be such a tool next time. I will install all the meters, and the house panel. Then we can restore power to the building that has been empty for 3 years.
|
Some boss you are, you didn't even know where to look for some pretty basic grounding requirements, tool.
__________________
There's only one way to succeed in anything, and that is to give it everything.
Vince Lombardi
|
|
|
08-10-2009, 11:27 PM
|
#48
|
|
Wanna be Guru
Join Date: Jan 2009
Location: Washington
Posts: 245
|
Quote:
Originally Posted by Magnettica
Some boss you are, you didn't even know where to look for some pretty basic grounding requirements, tool.
|
True. But ouch.
|
|
|
08-11-2009, 05:42 AM
|
#49
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by mikeg_05
True. But ouch. 
|
I dint have a book so I came on here to you people with no life.
|
|
|
08-11-2009, 04:53 PM
|
#50
|
|
Not Peter D
Join Date: Jan 2009
Location: USA
Posts: 5,416
|
Quote:
Originally Posted by gemini13
I dint have a book so I came on here to you people with no life.
|
Everyone is going to be so eager to help you now.
|
|
|
08-11-2009, 04:55 PM
|
#51
|
|
Not Peter D
Join Date: Apr 2009
Location: South Eastern MA
Posts: 2,908
|
Quote:
Originally Posted by gemini13
I dint have a book so I came on here to you people with no life.
|
I may not 'have a life' but I do know how to do my job.
|
|
|
08-11-2009, 05:54 PM
|
#52
|
|
Licensed Pro
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 2,784
|
Quote:
Originally Posted by Bob Badger
I may not 'have a life' but I do know how to do my job. 
|
Ditto that.
I was just thinking that I have no life but less than 2 weeks ago I tailgated with friends for over 4 hours, watched ACDC with 50,000 other metal maniacs, and on Friday night I'm going to a preseason NFL game.
Damn.... I really do have no life!
__________________
There's only one way to succeed in anything, and that is to give it everything.
Vince Lombardi
Last edited by Magnettica; 08-11-2009 at 07:51 PM.
|
|
|
08-11-2009, 07:56 PM
|
#53
|
|
Senior Member
Join Date: Feb 2008
Location: Atlanta, Ga/Hamilton, Al
Posts: 2,035
|
Why don't you own a code book, boss man? Life get in the way?
|
|
|
08-11-2009, 09:16 PM
|
#54
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by InPhase277
Why don't you own a code book, boss man? Life get in the way?
|
I do I didnt have it at my house. Thanks again TOOL
|
|
|
08-11-2009, 09:18 PM
|
#55
|
|
Not Peter D
Join Date: Jan 2009
Location: USA
Posts: 5,416
|
Quote:
Originally Posted by gemini13
I do I didnt have it at my house. Thanks again TOOL
|
Inphase277 is a redneck. 480sparky is a tool.
|
|
|
08-11-2009, 09:18 PM
|
#56
|
|
Junior Member
Join Date: Jan 2009
Location: Pennsylvania
Posts: 22
|
Quote:
Originally Posted by gemini13
I do I didnt have it at my house. Thanks again TOOL
|
I got my bid talk to power company as planned will start in a week 6,000 in a day for me. thanks
|
|
|
08-11-2009, 09:19 PM
|
#57
|
|
Licensed Pro
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 2,784
|
Settle down, Gemini, you can learn a lot here but you have to chill out a bit.
__________________
There's only one way to succeed in anything, and that is to give it everything.
Vince Lombardi
|
|
|
08-11-2009, 09:20 PM
|
#58
|
|
B4T Scotchkote installer
Join Date: Feb 2009
Location: Long Island, N.Y.
Posts: 4,466
|
Quote:
Originally Posted by gemini13
Thanks for your concern, you may try not to be such a tool next time.
|
A tool is a mechanical devise that makes a job easier.. better find a new word
|
|
|
08-11-2009, 09:21 PM
|
#59
|
|
Not Peter D
Join Date: Jan 2009
Location: USA
Posts: 5,416
|
Quote:
Originally Posted by gemini13
I got my bid talk to power company as planned will start in a week 6,000 in a day for me. thanks
|
 
|
|
|
08-11-2009, 09:25 PM
|
#60
|
|
Licensed Pro
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 2,784
|
$6000 in a day?
Hell, you could sub that baby out to me, I'll do it for $3000
__________________
There's only one way to succeed in anything, and that is to give it everything.
Vince Lombardi
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
|