Calculating AIC rating of Panel - Electrician Talk - Professional Electrical Contractors Forum
Old 06-03-2009, 06:29 PM   #1
TOU
Default Calculating AIC rating of Panel
Be nice..newby here..
I am working on a project with 600amp at the main. the main feeds 3 panels, each with 200amps. my question is, how do you calculate the AIC rating of these 3 200amps panel?
the main is 120/208v, 3phase and so are the panels. what do i need to look at? pls give example. thank you guys.
TOU is offline   Reply With Quote
Old 06-03-2009, 06:51 PM   #2
Well they do it with a program to calculate you need more info like feeder lengths wire size and if its copper or alu.
You need to tell us if its rigid conduit or alum or pvc or emt or underground or overhead the length is it parallel or a single run .
Next is this to be series rated or what 100 percent rating ?
Its kinda ohms law but just a little more info like the fault current of that transformer feeding the main panel needs to be known also ? lots of stuff there is a program you can get check out the web HANDBOOK OF ELECTRICAL POWER CALCULATION .
Take care
Old 06-03-2009, 07:05 PM   #3
TOU
i was actually hoping there is a way to do it by hand...i want to see the process
anyway, do you have the name of such a program?
Old 06-03-2009, 07:20 PM   #4
I believe its called a Current Fault Study or a cordination study done by a engineer .http://login.ecmweb.com/wall.aspx?ER...istic_fault%2F
Old 06-03-2009, 07:28 PM   #5
Rewards Points: 2,050
http://www.cooperbussmann.com/pdf/87...4e9d57d93c.pdf
Old 06-04-2009, 12:08 PM   #6
TOU
thank you guys..
De-Rating simplified? Electrician343 General Electrical Discussion 13 05-02-2009 11:15 AM
calculating resistance of a wire mike4089 General Electrical Discussion 6 02-11-2009 08:29 PM
Calculating hourly rate JohnJ0906 Business, Marketing, and Sales 17 11-04-2008 10:27 AM
need help calculating power loss john salyards General Electrical Discussion 16 03-12-2008 09:30 PM
calculating power loss john salyards NEC Code Forum 1 02-16-2008 07:40 AM