Originally Posted by RIVETER
I don't know what you mean. I've never considered "unbalanced magnetic fields", has anyone else?
This is an important point.
If the ground and neutral are connected at the main panel or upstream from it (meter base), then the bonded metal only forms a return path when a fault occurs from line to ground.
So if the fault occurs it should be cleared by the overcurrent device. In other words this is a temporary condition.
If you connect the ground and neutral down stream from the main panel as well as in the main panel, all bonded metal becomes part of the path for the neutral current. This is not a temporary condition, as described above, and it will have two direct consequences:
1) The current flowing through the bonded metal will cause it to warm up due to resistive heating.
2) Since the line and neutral return paths are not "tight" like they would be if all of the return current flowed in the neutral wire in the same reaceway or cable as the line wire, a wide-area magnetic field is formed. This field will induce currents in the bonded metal or any other conductor forming a closed path that encircles part of the wide-area magnetic field. The induced current will cause the metal to heat up. Eddy currents will also cause heating even if the metal does not encircle the magnetic field
I expect that there isn't enough current in most resi branch circuits to cause noticable resistive or inductive heating with improper ground/neutral connections. You might notice that an AM radio has a lot 60 Hz hum when tuned off station. Kinda like the first three way I wired
Because the small voltage drop across the metal sharing the neutral current, there wouldn't even be any touch potential.
EJPHI