I was thinking of just the 3 Conductors coming in from the POCO side, which that would be where they ground the B phase on the transformer bank. I would ground the meterbase the same as any other three-phase service. Am I thinking through this right?
Now I'm not sure what you are asking. In may area, the meter base is grounded somtimes and sometimes it isn;t. It is a call by the POCO. Ultimately it needs to be bonded to the neutral or g e system or the EGC but how it is done varies with the POCO.
the POCO will ground one corner of the delta. You also need to bond that same corner to the GEC and associated system.
the only time you use ground fault detectors is when it is an ungrounded delta, which I have not seen installed in a long time and will not be installed in any area I work in unless there is some overwhelming need for it (in other words, they aren;t installing them anymore around here)
Basically, all of this depends on what type of service is being supplied. You need to be sure it is a corner grounded and install as needed for that. I doubt you would be looking at an ungrounded delta anymore.