grounding a sub panel - Electrician Talk - Professional Electrical Contractors Forum
Old 05-16-2012, 07:03 PM   #1
Default grounding a sub panel
I am replacing a 40amp subpanel in a garage with a 100 amp subpanel.
the garage has an exsisting 1 in. conduit from the house. do i need a ground wire ran through that condiut if i am putting a new ground rod for the subpanel in the garage?
mbidingerres is offline   Reply With Quote
Old 05-16-2012, 07:12 PM   #2
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
depends on what kind of conduit.
The Following 2 Users Say Thank You to mcclary's electrical For This Useful Post:
leland (05-18-2012), Shockdoc (05-18-2012)
Old 05-16-2012, 07:14 PM   #3
just pvc underground, romex in house to main panel
Old 05-16-2012, 07:15 PM   #4
evil bastard
Rewards Points: 746
Unless you're still on '05 code, you need it then.
Old 05-16-2012, 07:17 PM   #5
which means then I have to increase the conduit from 1 in to 1-1/4 in
Old 05-16-2012, 07:19 PM   #6
evil bastard
Rewards Points: 746
maybe if you're running copper. If you're running al, you'll need 1.5"
Old 05-16-2012, 07:19 PM   #7
jza
Mad as Hell Member
jza's Avatar
Rewards Points: 2,302
You can increase it to 1 inch EMT and not have to run a grounding conductor inside the pipe, lol.
jza is offline   Reply With Quote
Old 05-16-2012, 07:23 PM   #8
it is 1 in pvc conduit right now but only underground
under concrete driveway. I was trying to avoid digging that up
Old 05-16-2012, 07:24 PM   #9
I am running copper # 2
Old 05-16-2012, 07:24 PM   #10
Awg-Dawg's Avatar
Rewards Points: 338
Id make it a 60a if I could.
99% of the time even the 60a is overkill.
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
The Following 6 Users Say Thank You to Awg-Dawg For This Useful Post:
BBQ (05-16-2012), leland (05-18-2012), mcclary's electrical (05-16-2012), nolabama (05-16-2012), The_Modifier (05-17-2012), user4818 (05-16-2012)
Old 05-16-2012, 07:27 PM   #11
Customer needs a 100 amp
Old 05-16-2012, 07:44 PM   #12
Awg-Dawg's Avatar
Rewards Points: 338
http://www.electrician2.com/calculat...alculator.html
Looks like your conductors work if you use #3 cu
The Following 2 Users Say Thank You to Awg-Dawg For This Useful Post:
Magnettica (05-17-2012), nolabama (05-16-2012)
Old 05-16-2012, 09:11 PM   #13
Rewards Points: 5,198
The ground rod would be for lightning...you still need the equipment ground from the main panel to the second building.
Old 05-16-2012, 09:42 PM   #14
fanelle's Avatar
Rewards Points: 154
You could use a wire with a higher insulation tempature rating like a Z or a TFE. Then your conductor size would shrink you could use the same size pipe and be code compliant. However it is probally going to cost about a dollar more per foot or so.
fanelle is offline   Reply With Quote
Old 05-16-2012, 10:10 PM   #15
mbednarik's Avatar
Rewards Points: 1,054
most pvc is rated 90c. Also the terminations are still 75 or 60 c rated. Does it need a full size neutral? What is the calulated load?
mbednarik is online now   Reply With Quote
Old 05-17-2012, 01:02 AM   #16
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
First of all, you need to look in chapter 9 of the NEC for the correct size area of conduit.
Then you need to determine the size of the conductors you'll be using, and compare them to the size conduit you have.
Third, you're going to need a lot of lube to pull (2) #3 coppers, (1) #6 copper, and (1) #8 copper equipment grounding conductor.
Fourth, don't forget about your ground rod (required) and the (6) disconnect rule.
Replies based on NEC 2014
Old 05-17-2012, 12:12 PM   #17
Well It is only 25 ft and one 90 and it is fed from a 100amp breaker from the main panel so if i an right i shouldn't need a main in this panel
Old 05-17-2012, 12:58 PM   #18
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
The issue is if you have more than (6) circuit breakers a "main" circuit breaker must be installed.
NEC 225.33 Maximum Number of Disconnects.
Old 05-18-2012, 12:12 AM   #19
Rewards Points: 1,062
Not if it's a sub panel like the OP was talking about changing. That only applies to the main service
ElectricJoeNJ is offline   Reply With Quote
Old 05-18-2012, 12:30 AM   #20
wendon's Avatar
Rewards Points: 50
If the sub-panel is in a different structure with over 6 disconnects, you'll need a main disconnect.
wendon is online now   Reply With Quote
The Following 3 Users Say Thank You to wendon For This Useful Post:
frenchelectrican (06-27-2012), leland (05-18-2012), Magnettica (06-21-2012)
Grounding Electrodes For Each Panel? scityelectric Commercial Electrical Forum 12 05-18-2011 01:30 AM
sub panel grounding sparkmaster 1 Services and Service Equipment 2 06-07-2010 12:34 PM
Grounding a new panel subelect General Electrical Discussion 10 12-31-2009 10:54 PM
Multiple panel grounding waco General Electrical Discussion 11 07-16-2009 07:18 PM
Grounding the panel door JBIRD General Electrical Discussion 12 04-13-2008 08:09 AM