Old 06-04-2009, 12:18 PM   #1
TOU
Default how do you calculate VA for a motor?
thanks in advance guys, again , be nice...fresh out of college here..
i'm trying to calculate the KVA of an elevator motor, 20 horse power, 120/208, 3phase. i'm looking at the spec now, but confused on the info.
there are "rated ac amp" = 65.1amps
across the line starting ac amp = 391,
wye-delta start ac amp = 195",
solid state starting ac amps = from 130-295, min-max
THESE AMPS HERE ARE UNDER THE "MOTOR NAMEPLATE AND STATING DATA"
and then there are other columns under "FULL LOAD UP SPEED"
motor ac amps = 91
control trans ac amps = 4
total ac amps = 95.
which of these numbers do i use to calculate the KVA (i'm doing a load summation for a panel)
TOU is offline   Reply With Quote
Old 06-04-2009, 03:23 PM   #2
20hp x 746/208v x 99.46%eff x ?pf x 1.73
i need the power factor
how many kw?
sparkyboys is offline   Reply With Quote
Old 06-04-2009, 04:02 PM   #3
TOU
i am not sure, the spec says nothing about kw....
it seems the formula you're using is totally new to me...or maybe i forgot my formulas...but i thought
va = 208*1.732*(the amp...one of those amp given in the spec)...am i attacking this thing wrong?
Old 06-04-2009, 04:10 PM   #4
oh my bad
208 x 65.1 x 1.73/ 1000=23.425584 va
had to change answer, i divided by 100 instead of 1000, sorry.
this is correct tho
Old 06-04-2009, 07:37 PM   #5
TOU
thanks...
by the way, is there any time when you use 95 instead of 65?
Old 06-04-2009, 07:43 PM   #6
I think it's awesome that they give you the across-the-line starting amps and wye-delta starting amps. That's great information to have when you're sizing a panel, feeder, or a service. Pretty rare information to come across. Nothing like winking everyone's lights every time some calls the elevator.
Old 06-04-2009, 07:45 PM   #7
By the way, I'd use the "running at full load going up" amp listing in the watt calc. That's going to be your worst case scenario, which is sorta the whole reason you're probably calculating KVA.
Old 06-04-2009, 09:25 PM   #8
Originally Posted by TOU View Post
thanks...
i always use 75. use 95 when derating, especially when ambient temps are above 30 deg C, like for ridgid conduit on a roof that unprotected by sunlight.
mostly will use 75 90% of the time. most lugs are rated for 75. rarly use 65
Old 06-04-2009, 09:41 PM   #9
captkirk's Avatar
tony Likes this thread....good refresher info
Old 06-05-2009, 03:01 AM   #10
so would that be the 91a or the 91a + 4a?
never done an elevator before, GC always has elevator crew do that.
Old 06-05-2009, 12:07 PM   #11
TOU
in summary from all of your comments....
use 65 for quick and dirty calcs..
use 75 (where did this number come from?)
and use 95 for safest calcs..
am i correct so far?
another thing...why is it wrong to just use 20hp and convert that into kva?
Old 06-05-2009, 12:57 PM   #12
75 is lug rating. i do not understand what you are asking in the rest of your post
Old 06-07-2009, 09:50 PM   #13
Calculating the KVA here is really simple. Use the stuff under 'full load up speed'. Everything else is useless.
You'll need to do two calculations. The first is the motor. Multiply the amps by the voltage, and since it's 3 phase, multiply the result by 1.73. This is VA. Divide by 1000 to get KVA.
Next, assuming the control transformer is single phase, multiply the volts by the amps. The result is VA. Divide by 1000 to get KVA.
On one leg, you'll have the motor only. On the other two, you'll have the motor plus the controls.
Rob
Old 06-08-2009, 04:33 PM   #14
Licensed Pro
Magnettica's Avatar
motor ac amps = 91
total ac amps = 95.
A 20 HP motor at 208 volts 3Ø is 59.4 amps.
Vince Lombardi
Old 06-08-2009, 05:23 PM   #15
steelersman's Avatar
He wasn't asking about degrees celcius columns in table 310.16. He was asking about the 2 different as amps values given on the nameplate.
I wasn't aware that there was a 95 degree column in the code book. I thought it was 90 degrees. Not sure what codebook you're looking at.
Also there's no 65 degree column either. It's 60.
Old 06-08-2009, 05:26 PM   #16
you'd better take sparkyboys posts with a grain of salt then cause that boy sounds like he's back on the weed again.
Old 06-08-2009, 06:46 PM   #17
who cares. i got better answers from mike holt site anyways
Old 06-08-2009, 06:49 PM   #18
Not Peter D
You didn't capitalize this sentence and you truncated "because" into "cause."
Old 06-08-2009, 08:27 PM   #19
you weren't the one looking for an answer now were you. So crack open that NEC, put the bong down and start reading!
Old 06-08-2009, 08:29 PM   #20
Sometimes when I'm speaking to a redneck, I like to speak the same as them.
480 motor help please. gardner General Electrical Discussion 24 08-19-2009 08:20 PM
How do I calculate VD and what effects would less V have on a House? Jeff000 General Electrical Discussion 16 04-11-2009 11:27 PM
motor Bkessler NEC Code Forum 14 07-27-2008 08:53 AM
dc motor GREGNC General Electrical Discussion 1 12-19-2007 06:44 PM
calculate sizes and type of wiring systems kevruta NEC Code Forum 3 02-26-2007 06:05 PM