05-29-2008, 10:36 PM
Load Calc. for Old Single Family Dwellings
Can anyone tell me the best way/formula to use when doing a load calc. on a old house(40+). The customer wants to add a refrigerated air unit to their home. The house is 2000 Sq. Ft with only the Dryer being on a electric circuit. The Water Heater and Stove are gas. The Main Panel is rated at 100 Amps and was installed when they extended the Sq. Footage of their home.
Basically, I want to know what is the biggest refrigerated unit I can install without providing them with a new service upgrade?
Thanks in advance,
Reseman
05-29-2008, 10:47 PM
Seen your member
The age of the house has no bearing on a load calculation.
To anything!
05-30-2008, 06:46 AM
"A" inside wireman
Thanks in advance,
Reseman
Exactly what is your electrical trade?
"One Nation Under God"
05-30-2008, 10:04 AM
Reseman
My suggestion is to use Article 220, Branch-circuit, feeder, and service calculations. Also, see 220.16(A)(2). Basically, treat the house as being new.
05-30-2008, 10:04 PM
So what do you guys do....Do you count all the existing fixtures, outlets, appliances, etc. or do you guys just calculate it as a new house?
05-31-2008, 10:21 AM
You can do a standard 220 calculation, or use 220.83
John from Baltimore