Old 11-11-2010, 12:24 PM   #1
Default Panel board sizing
This question kind of approaches this subject from the back side.
I have a project where there is a 480vac drop, but no panel boards. We want to install a transformer and panel board to get 120/208 for general use receptacles.
The drop is 480vac/100amp. I back calculated the maximum transformer size to be 83KVA. We'll use a 75KVA. The secondary will be about 200amps, if I did my calculations correctly.
The question is this. Based on this information, what is the maximum panel board size that I can attach to this service?
backintheblue is offline   Reply With Quote
Old 11-20-2010, 06:21 PM   #2
225 amp @ 208/120 3 pf
Old 11-20-2010, 06:30 PM   #3
Chief Electron Relocator
Originally Posted by backintheblue View Post
..........The drop is 480vac/100amp. ......... what is the maximum panel board size that I can attach to this service?
100amps?
Old 11-20-2010, 08:48 PM   #4
PGW Professional
Magnettica's Avatar
Don't worry too much about what the POCO is is supplying you with now. Provide them with a real load calculation and they will determine which size wires to run to your service.
But for kicks... (I x E = P)
(480V x 1.732) x 100 amps = 83Kva
83,000va/ (208V x 1.732) = 231 amps
Looks like you're good to go with what's there but you'll still need to supply the calc load to the poco.
Old 11-22-2010, 10:47 PM   #5
I second this suggestion. I guess,it is safe enough.
alyna is offline   Reply With Quote
Old 11-23-2010, 08:05 AM   #6
You can attach any size panelboard you want it is the OCPD that makes the difference.
Old 11-23-2010, 10:41 AM   #7
Ax grinder
raider1's Avatar
As long as the rating of the panelboard meets or exceeds the rating of the overcurrent protective device protecting the panelboard.
Chris
Old 12-05-2010, 06:45 PM   #8
Second the motion
wayne g is offline   Reply With Quote
Sizing Main Disconnect For Control Panel? Voltshead Services and Service Equipment 8 01-21-2011 05:39 AM
Hello All, new to board. G-man Introductions 20 12-30-2009 09:08 PM
Newbie to board adnoh Introductions 27 12-13-2009 06:45 AM
Hi New to Board wiremanz Introductions 6 09-03-2009 08:18 AM
panel board / meter advice hodaire UK Electrical Forum 7 04-30-2009 05:36 PM